Depending on the applicable edition of NFPA 14 you may have to use two PRV's in series with bypass instead of just one but is still okay to do. You need to check NFPA 14, I believe it changed to require two PVC's in series in 2007. If you're on 2004 only one valve is required.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Thursday, May 05, 2011 1:51 PM To: [email protected] Subject: Re: Pressure reducing valves in pump discharge If I recall correctly, you can't have the PRedV before the pump discharge valve as NFPA 20 does not allow PRedV's. However, NFPA 13 does, so by placing it after the pump discharge shut off valve, you are now in NFPA 13 territory and not NFPA 20 territory. A.4.7.7.2 It is not the intent of this subsection to restrict the use of pressure reducing valves downstream of the discharge isolation valve for the purpose of meeting the requirements of 4.7.7. 4.7.7.1 The net pump shutoff (churn) pressure plus the maximum static suction pressure, adjusted for elevation, shall not exceed the pressure for which the system components are rated. 4.7.7.2* Pressure relief valves and pressure regulating devices in the fire pump installation shall not be used as a means to meet the requirements of 4.7.7.1. On 5/5/2011 1:42 PM, Bobby Gillett wrote: > We have a project where the combined pressure of the pump/water supply > necessary to supply the standpipe/system demand will create a pressure > greater than 175psi at churn (around 200). The engineer is suggesting a > single 6" pressure reducing valve on the discharge side of the pump, > directly after the pump and before the check valve, to keep all downstream > system/standpipe piping from exceeding the 175psi mark. (It is a 750gpm pump > so suction and discharge piping is 6"). I don't see any reference in NFPA 20 > to pressure reducing valves for anything other than Steam Turbine Drive. > Does this scenario sound accurate and can this be installed at the above > mentioned location as long as it is installed per the requirements of > NFPA13-2007 8.16.1.2 and the set pressure of the relief valve still allows > full system/standpipe demand? The engineer has said he has done this many > other times in various states. > > > > Thank you, > > > > Bobby Gillett > > Sr. Project Manager > > Key Fire Protection, Inc. > > (731) 424-0130 office (731) 424-9285 fax > > (731) 267-4853 cell > > <mailto:[email protected]> > [email protected] > > > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)