We have a project where the combined pressure of the pump/water supply necessary to supply the standpipe/system demand will create a pressure greater than 175psi at churn (around 200). The engineer is suggesting a single 6" pressure reducing valve on the discharge side of the pump, directly after the pump and before the check valve, to keep all downstream system/standpipe piping from exceeding the 175psi mark. (It is a 750gpm pump so suction and discharge piping is 6"). I don't see any reference in NFPA 20 to pressure reducing valves for anything other than Steam Turbine Drive. Does this scenario sound accurate and can this be installed at the above mentioned location as long as it is installed per the requirements of NFPA13-2007 8.16.1.2 and the set pressure of the relief valve still allows full system/standpipe demand? The engineer has said he has done this many other times in various states.
Thank you, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)