We have a project where the combined pressure of the pump/water supply
necessary to supply the standpipe/system demand will create a pressure
greater than 175psi at churn (around 200). The engineer is suggesting a
single 6" pressure reducing valve on the discharge side of the pump,
directly after the pump and before the check valve, to keep all downstream
system/standpipe piping from exceeding the 175psi mark. (It is a 750gpm pump
so suction and discharge piping is 6"). I don't see any reference in NFPA 20
to pressure reducing valves for anything other than Steam Turbine Drive.
Does this scenario sound accurate and can this be installed at the above
mentioned location as long as it is installed per the requirements of
NFPA13-2007 8.16.1.2 and the set pressure of the relief valve still allows
full system/standpipe demand? The engineer has said he has  done this many
other times in various states.

 