This, much like the water supply question earlier, sounds like a "Missouri 
letter" situation.  Missouri being the show-me state of course, without an 
enforceable code to back it up, it's just "what someone wants".  The BFV has to 
have the valves either monitored or chained open, and frankly the FDC should be 
upstream of any such control valves allowing the fire department to put water 
on the system even if some bonehead did close the thing.
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.439.2695
www.bmwc.com

________________________________

From: [email protected] on behalf of Brian Harris
Sent: Mon 5/16/2011 3:44 PM
To: [email protected]
Subject: Wall Post Valves



Could somebody explain to me the need of a wall post valve downstream of a
DCVA inside a building? I'm being told it has to be there in case somebody
accidentally closes the valve on the BFP so the responding fire department
would not have to go inside the burning building to turn the water on... I
ain't making this stuff up.



Brian Harris, CET

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476







=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17450)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to