I've known dumb engineers and I've don some dumb engineering but I find it hard to believe that an engineer thinks this arrangement would solve the stated problem: restoring water flow by opening a valve downstream of a closed valve. At first I thought it was an renegade AHJ requirement and that I can believe. I'm now thinking that there is a community requirement for the PIV so that the control valve is operable from the exterior. For it to be downstream of the DCVA makes sense also since the fire system, even on a dedicated fire line, is not part of the fire system until it leaves the double check. This is the left hand not knowing what the right is up to (or each being controlled by different brains) so that the FD wants to be able to control the water supply from outside the building, hence the PIV style control valve arrangement. But for this to work the DCVA needs to be outside also, so all valves are accessible. The water purveyor on the other hand may want the DCVA inside, or perhaps the engineer is saving the client the cost of the vault while meeting the letter of the code, if not its spirit. Too much local rules and second guessing to be definitive with the knowledge at hand but if the engineer really thinks the PIV is going to accomplish something more than meeting a local ordinance then he probably find more suitable work. Male nurses are in demand, as are pizza assemblers.
On Tue, May 17, 2011 at 6:06 AM, Gregg Key <[email protected]> wrote: > Brian, You can buy a DCVA with a PIV installed on the bottom of it. We have > used it in the past to meet that requirement > > C.Gregg Key, SET > Key Fire Protection Services,Inc > Project Manager > (O) 706-790-3473 > (C) 706-220-8821 > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Brian > Harris > Sent: Tuesday, May 17, 2011 8:42 AM > To: [email protected]; [email protected] > Subject: RE: Wall Post Valves > > The engineer wants the DCVA then the PIV, then the FDC. > > Brian Harris, CET > FDFP Inc. > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Tuesday, May 17, 2011 7:48 AM > To: [email protected]; [email protected] > Subject: Re: Wall Post Valves > > That's what I was thinking but then they would want another backflow on > that > connection. It would be the never ending story. > > Mike > Sent on the SprintR Now Network from my BlackBerryR > > -----Original Message----- > From: "steve" <[email protected]> > Sender: [email protected]: Mon, 16 May 2011 > 20:24:15 > To: AFSA<[email protected]> > Reply-To: [email protected], [email protected] > Subject: Re: Wall Post Valves > > I think you meant DOWNSTREAM for the FDC, no? > > I'm assuming that the BFP in question is inside the building ... The point > of a wall PI downstream of a BFP would be to allow outside control of the > water supply without having to enter. Same as an underground PIV. In wood > or metal stud construction you can use a butterfly wall indicator as well. > Another application for wall indicators is to provide outside control of > sectional riser valves. > > But if the original question relates to a single system with an outside > BFP, > then I'm with you on the "Missouri" approach. > > SL > > > > Sent from my Verizon Wireless BlackBerry > > -----Original Message----- > From: "Morey, Mike" <[email protected]> > Sender: [email protected] > Date: Mon, 16 May 2011 15:49:07 > To: <[email protected]> > Reply-To: [email protected] > Subject: RE: Wall Post Valves > > This, much like the water supply question earlier, sounds like a "Missouri > letter" situation. Missouri being the show-me state of course, without an > enforceable code to back it up, it's just "what someone wants". The BFV > has > to have the valves either monitored or chained open, and frankly the FDC > should be upstream of any such control valves allowing the fire department > to put water on the system even if some bonehead did close the thing. > > Mike Morey, SET, CFPS > Sprinkler Designer > BMW Constructors, Inc. > O: 317.651.0596 | C: 317.439.2695 > www.bmwc.com > > ________________________________ > > From: [email protected] on behalf of Brian Harris > Sent: Mon 5/16/2011 3:44 PM > To: [email protected] > Subject: Wall Post Valves > > > > Could somebody explain to me the need of a wall post valve downstream of a > DCVA inside a building? I'm being told it has to be there in case somebody > accidentally closes the valve on the BFP so the responding fire department > would not have to go inside the burning building to turn the water on... I > ain't making this stuff up. > > > > Brian Harris, CET > > First Defense Fire Protection > > 11957 Ramah Church Road > > Huntersville, NC 28078 > > Phone: 704.948.3506 > > Fax: 704.948.3507 > > Nicet # 128476 > > > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17450) > http://www.pctools.com/ > ======= > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17450) > http://www.pctools.com/ > ======= > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17450) > http://www.pctools.com/ > ======= > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
