Looking for some other forum experience here. How have you been dealing
with architects and GC's that state the IBC does not require draft stops
in an attic, so they are not willing to put them in when the CC heads
are req'd and the CC heads require a draft curtain to be installed?
On 6/6/2011 9:23 AM, Matt Grise wrote:
I agree. Just looked at that this morning. The handbook elaborates that testing
has found standard sprinks to be ineffective in short flat comb concealed
spaces.
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116
*Licensed in KS& MO
913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson, Duane
(NIH/OD/ORS) [C]
Sent: Monday, June 06, 2011 11:22 AM
To: '[email protected]'; '[email protected]'
Subject: RE: CC1/CC2 or COIN sprinklers
Yes. See 8.15.1.6 (2007).
Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services
National Institutes of Health
301-496-0487
"Protecting Science - One Sprinkler at a Time"
-----Original Message-----
From: Travis Mack, SET [mailto:[email protected]]
Sent: Monday, June 06, 2011 12:08 PM
To: [email protected]
Subject: CC1/CC2 or COIN sprinklers
Trying to settle a "discussion" here. When you have a flat concealed
combustible space and<36" of clearance, are the specially listed heads
required?
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)