For IBC (2009 NJ Edition in my case), 404.3, look at the exceptions. Section
404.2 is more for the architect.

For NFPA (2007) 8.15.4.4 is significant if the opening is greater than 20' x
20'.


Richard

On Tue, Jun 7, 2011 at 9:15 AM, Dewayne Martinez <[email protected]> wrote:

> Is there anywhere in the IBC/ NFPA codes that talks about elimination of
> sprinklers at high ceilings/atriums.  I have a building with 82' high
> atrium and need to know how to address.
> Thanks,
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI