Thanks Richard, That was exactly what I was looking for. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richard Lindner Sent: Tuesday, June 07, 2011 8:20 AM To: [email protected] Subject: Re: Atrium - high ceilings
For IBC (2009 NJ Edition in my case), 404.3, look at the exceptions. Section 404.2 is more for the architect. For NFPA (2007) 8.15.4.4 is significant if the opening is greater than 20' x 20'. Richard On Tue, Jun 7, 2011 at 9:15 AM, Dewayne Martinez <[email protected]> wrote: > Is there anywhere in the IBC/ NFPA codes that talks about elimination > of sprinklers at high ceilings/atriums. I have a building with 82' > high atrium and need to know how to address. > Thanks, > Dewayne Martinez > Design Build Fire Protection > New Berlin, WI > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)