For IBC (2009 NJ Edition in my case), 404.3, look at the exceptions.
Section
404.2 is more for the architect.

For NFPA (2007) 8.15.4.4 is significant if the opening is greater than
20' x 20'.


Richard

On Tue, Jun 7, 2011 at 9:15 AM, Dewayne Martinez <[email protected]>
wrote:

> Is there anywhere in the IBC/ NFPA codes that talks about elimination 
> of sprinklers at high ceilings/atriums.  I have a building with 82' 
> high atrium and need to know how to address.
> Thanks,
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to