I disagree with the consensus here: 2007 ed.
8.6.5.2.1.2 Regardless of the rules of 8.6.5.2 [THREE TIMES RULE] , solid continuous obstructions shall meet the applicable requirements of 8.6.5.1.2.[SOFFIT RULE] Further, 8.6.5.2.1.4* For light and ordinary hazard occupancies, **structural members only** shall be considered when applying the requirements of 8.6.5.2.1.3 [THREE TIMES RULE]. Even Further there is the appendix which explains the intent of the three times rule. On Thu, Jun 16, 2011 at 11:35 AM, Bob <[email protected]> wrote: > Brian, > Soffit rule applies when beam rule cannot. > > Bob Knight, CET III > 208-318-3057 > www.firebyknight.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Brian > Harris > Sent: Thursday, June 16, 2011 8:53 AM > To: [email protected] > Subject: Obstruction to Discharge > > Looking for an outsiders opinion to settle an in-house debate. Looking at a > project that has a 12'-0" suspended ceiling and along one wall has a 9'-0" > soffit, this soffit is 34" deep. One side of the debate says that since > it's > a soffit and against a wall that 8.8.5.1.2(b) would apply but since this > soffit is over 30" wide heads would need to be added at the 9'-0" ceiling. > The other side of the debate says that as long as you can get far enough > away from the edge of the soffit as shown in 8.8.5.1.2(a) then heads would > not need to be added. What says the forum? > > > > Brian Harris, CET > > First Defense Fire Protection > > 11957 Ramah Church Road > > Huntersville, NC 28078 > > Phone: 704.948.3506 > > Fax: 704.948.3507 > > > > > > > > ======= > Email scanned by PC Tools - No viruses or spyware found. > (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17700) > http://www.pctools.com/ ======= > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)