see nfpa 13:  8.6.4.1.1.3 (2007)

On Fri, Jul 8, 2011 at 6:07 AM, Brian Harris <[email protected]>wrote:

> NFPA 2007 8.8.5.1.2(2) allows for sprinklers to be placed on opposite sides
> of an obstruction that is less than 4' wide as long as the centerline of
> the
> obstruction to the sprinkler does not exceed 1/2 the allowable distance
> between sprinklers....
>
> I have a soffit that that is 3'-6" wide that runs around the perimeter of a
> gwb ceiling on one side and on the other side is open to the deck. From the
> gwb ceiling down to the bottom of the soffit is 36" & from the deck down to
> the bottom of the soffit is 96".
>
> Would this section of code allow the omission of any sprinklers in the
> soffit itself?
>
> Brian Harris, CET
> First Defense Fire Protection
> 11957 Ramah Church Road
> Huntersville, NC 28078
> Phone: 704.948.3506
> Fax: 704.948.3507
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17860)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to