I don't think you have to include outside hose flow. But, you said this was 
military. As such, you will most likely have a separate test header with (1) 
2.5" hose vale for every 250 gpm system demand. That has at least been my 
experience. 
 
Travis Mack, SET
MFP Design, LLC
www.mfpdesign.com

Sent on the Sprint® Now Network from my BlackBerry®

-----Original Message-----
From: "Gregg Key" <[email protected]>
Sender: [email protected]: Tue, 21 Jun 2011 10:35:36 
To: <[email protected]>
Reply-To: [email protected]
Subject: Backflow forward flow test 

Ok now that I got past that, Any reason that the 2" main drain could not be
used if the required flow could be achieved. System demand + hose allowance?