The reason that we have used the butterfly valve as opposed to flipping the
check on the FDC is for the annual testing as well.  In NFPA25, 2008
edition, 13.6.2 calls for forward flow testing annually.  In order to flip
the check you will need to shutdown and drain systems first to flip it, then
energize and flow, then drain down and return to original position.  



Jarron J. Gass - J. & J. Fire Protection Co., Inc.
101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151
emergency (724) 898-2481, [email protected], www.jandjfire.com 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, June 21, 2011 10:52 AM
To: [email protected]
Subject: RE: Fire Dept Test Port reference

Can't you just flip the check valve and pull the FDC?


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Gregg Key
Sent: Tuesday, June 21, 2011 10:31 AM
To: [email protected]
Subject: RE: Fire Dept Test Port reference

WOW , He sent word that the reference is ....NFPA 13 2010
ed.....A.8.17.4.6.1 

A.8.17.4.6.1 The full flow test of the backflow prevention valve can be
performed with a test header or other connection downstream of the valve. A
bypass around the check valve in the fire department connector line with a
control valve in the normally closed position can be an acceptable
arrangement....

So he was talking about Backflow. No word on the sign

C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Smith, Steven
D. (CSFD)
Sent: Tuesday, June 21, 2011 10:03 AM
To: [email protected]
Subject: RE: Fire Dept Test Port

If they are so insistent, have them provide the reference in 13 for you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to