The reason that we have used the butterfly valve as opposed to flipping the check on the FDC is for the annual testing as well. In NFPA25, 2008 edition, 13.6.2 calls for forward flow testing annually. In order to flip the check you will need to shutdown and drain systems first to flip it, then energize and flow, then drain down and return to original position.
Jarron J. Gass - J. & J. Fire Protection Co., Inc. 101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151 emergency (724) 898-2481, [email protected], www.jandjfire.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of George Church Sent: Tuesday, June 21, 2011 10:52 AM To: [email protected] Subject: RE: Fire Dept Test Port reference Can't you just flip the check valve and pull the FDC? George L. Church, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Gregg Key Sent: Tuesday, June 21, 2011 10:31 AM To: [email protected] Subject: RE: Fire Dept Test Port reference WOW , He sent word that the reference is ....NFPA 13 2010 ed.....A.8.17.4.6.1 A.8.17.4.6.1 The full flow test of the backflow prevention valve can be performed with a test header or other connection downstream of the valve. A bypass around the check valve in the fire department connector line with a control valve in the normally closed position can be an acceptable arrangement.... So he was talking about Backflow. No word on the sign C.Gregg Key, SET Key Fire Protection Services,Inc Project Manager (O) 706-790-3473 (C) 706-220-8821 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Smith, Steven D. (CSFD) Sent: Tuesday, June 21, 2011 10:03 AM To: [email protected] Subject: RE: Fire Dept Test Port If they are so insistent, have them provide the reference in 13 for you. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)