The louvers are one of the thoughts I had for this (I referred to it as a 
grate). The additional minimum temperature is probably a good idea. Since this 
is a primary residence for the owner, I don't think that would be much of a 
problem.  Installing any ductwork within the joist space is not practical (plus 
I told him full insulation on both sides). The HSWs will not work due to the 
geometry of the space.



At 11:52 AM 6/24/2011, you wrote:
>As Ron say's "Heat Loss" We have handled this similar to what you propose
>with two exceptions. To promote "Positive" heating of the branch line, we
>had a 6x12 open louver installed at the low end of the "chase" (joist space)
>and at the high end. Then convection did the rest. We also sent a CYA letter
>stating that our design required that the space heating maintain a minimum
>of 60'F as opposed to the 40'F allowed by NFPA. We made sure to state that
>freezing could occur if there was any failure of the heating system during
>the heating season.
>
>Also due to another issue that has occurred with this type of installation,
>require the GC to insure that there are no ducts or exhaust duct (bathroom
>exhaust or kitchen hood)allowed in this or the adjacent joist space. (Those
>little flappy back-draft dampers tend to stick open allowing cold air back
>into the unit, if it's near your pipe it will freeze.)
>
>Lastly, is there a reason you're not looking at HSW heads "Down the slope"
>spray pattern? We have used these in the past to avoid exactly what your
>doing.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Ron Greenman
>Sent: Friday, June 24, 2011 8:24 AM
>To: [email protected]
>Subject: Re:
>
>The question becomes what is the heat loss through the insulation in
>relation to the heat gain in the room. Presume no insulation and the roof is
>still a barrier and still has a R value. So if my heat loss is X.zero and my
>input (at the same point) is equal to (1) X.zero or increased to (2)
>X.something and my starting temperature was 70F then I will maintain
>(scenario (1)) or increase (scenario 2)) the temperature at that point in
>the room. An ice cave is a shelter because it protects your body from the
>wind which conducts heat away from your heat engine (metabolism) and
>confines the air space around you and insulates that space from rapid heat
>transfer to the larger environment, hence lessening the your radiant heat
>loss. It's all about the thermal balance. Now back to the Ashram.
>
>On Fri, Jun 24, 2011 at 7:09 AM, Todd Williams <[email protected]> wrote:
>
>> I am working on a small mixed-use building with commercial space on the
>> first floor and an apartment with loft above. Part of the apartment has a
>> cathedral ceiling, which needs to have sprinklers on the slope. No other
>> options. The roof is framed with 2x10s and they plan to use a spray in
>foam
>> insulation the entire depth of the joists. My thought was if they took one
>> joist bay and only put 5" of insulation and create a space to run the
>pipe.
>> Would that be sufficient to prevent pipe from freezing? I also thought
>about
>> putting a small grate at the bottom and top of the channel to allow heat
>to
>> flow into the space. Has anyone done anything like that before? Thoughts
>on
>> weather it would work? Not a lot of options and I don't want to go with an
>> antifreeze system
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
>-- 
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
>They are happy men whose natures sort with their vocations. -Francis Bacon,
>essayist, philosopher, and statesman (1561-1626)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to