No draft stops yet. This is an afterthought. However, the 18" dimension might 
end up below the minimum ceiling height required by Code.


At 10:21 AM 6/29/2011, you wrote:
>Is a draft stop present, 2007 NFPA-13 8.15.4 ?
>
>John Drucker Jr CET
>Fire Protection Subcode Official
>Fire/Building/Electrical Inspector
>Borough of Red Bank, NJ  
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd
>Williams
>Sent: Tuesday, June 28, 2011 5:41 PM
>To: [email protected]
>Subject: water curtain and QR reduction
>
>I am working on a project where we have and open space with ceilings of
>various heights up to 9 ft. In one part of the building we have an open
>stair to the floor above. (the upper floor is going to be sprinklered in
>the next phase. this is an existing college library.)  The Fire Marshal
>has asked for a water curtain around the stairway. Does the presence of
>this stairway negate the application of the QR reductions? If so, would
>a water curtain alter that? How far from the opening would the design
>area need to be to allow the reduction?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>CONFIDENTIAL AND PROPRIETARY:
>This email message is intended only for the use of the individual or entity to 
>which it is addressed and may contain information that is privileged and 
>confidential, nor is it, unless specifically stated, intended to be relied 
>upon by any person or persons other than the individual or entity named above 
>and no warranties or representations are made or intended to persons or 
>entities not named above.  If the reader is not the intended recipient, you 
>are hereby notified that any dissemination, distribution or copying of this 
>communication is strictly prohibited.  If you have received this communication 
>in error, please notify us immediately by telephone, return this message to 
>the address above and delete all copies.  Thank you.
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to