You're crossing into a nebulous area when you attempt to connect reality and methodology (better known as the twilight zone where the whole court is out of order). In the same vane, we could debate the fact that 80+% of fire are controlled by no more than 3 sprinklers and ask why have a 1500 sf remote area (or even 900 sf with QR). Bottom line is that we have X amount for sprinkler (that exceed the actual demand) and a simultaneous Y amount for hose demand (for those cases that have some mop-up) producing the only reality that counts - that being that it works. Occasional variances are granted to reduce the hose demand but in looking at it, I'm having a difficult time connecting those dots. What is the relevance of having 1500 gpm hose demand when discussing the ability to supply the sprinkler and a reduced hose demand unless you plan to turn off the sprinklers and run only a manual response? Apples to oranges. I Like them both but not together.

Roland

On Jun 30, 2011, at 8:43 AM, Ron Greenman wrote:

It was just rhetorical. I was thinking what if I'm boosting the tank
pressure to just what I need (think steepish curve) to operate the sprinks at the 450 gpm. That gets the 1500 gpm to the hydrant at over 0 psi and the engine takes it to whatever the FD wants. So I'm showing a steep drop in pressure with supply and a rise in demand to almost the magic line. Then I have to add the horizontal 250 gpm and I'm slightly north of the supply curve. Easy enough to fix with a better designed pump but why should I have to fix it? As for gpm the tank has sufficient capacity to cover duration for both hydrant and system operating simultaneously so I meet that water supply quantity demand in spades. Why do I need to include that 250 gpm when I have more than enough water for simultaneous operation? What if that pump that will do the job without adding the hose stream is cheap and forcing the addition of the hose stream increases my cost? Why do I need to spend the money for a different pump to flatten a curve that meets need? And why do I need to add it if I have one tank but not if two tanks? This has mostly to do with what is on the piece of paper and that horizontal line from 450 gpm
to 700 gpm and how that interacts with the other diagonal line heading
downhill and to the right. The pump is undersized to cover the pressure at the gpm required when this extra and arbitrary 250 gpm is added to the curve
but the 250 gpm is covered by the 1500 gpm and engine psi boost at the
hydrant, and would be OK if each was supplied by it's own tank (the hydrant is only on the pump because it and the building and a future building are 10 feet higher than the base of the tank and the the single pump (which will be sized to handle the extra code required 250, but the tank is oversized and capacious enough to cover both buildings burning and using the hydrant at the same time for an hour) is the cost-effective. It just struck me as one
of those things that could happen (the supply pressure issue).

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to