Ok.  Then use standard response heads for the clouds.  It sounds like this
is a renovation to an existing building so you have 2 options as I see it.

1) NFPA 13-8.3.3.1 (2007 ed) option #3 - this allows you to use S/R heads in
a modification to an existing system where S/R heads are already installed
2) NFPA 13-8.3.3.2 (2007 ed) Change all the heads in the compartment to Q/R.
If it's not a big compartment this is the way I would go for life safety
reasons.  If it is too big and would become a financial burden to the owner,
then see #1 above.

This is simply my opinion and may not be correct :)

Cliff Whitfield, SET
President
Fire Design, Inc.
850-526-1886
 


[email protected]
www.fire-design.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, July 12, 2011 7:20 PM
To: [email protected]
Subject: RE: QR sprinklers and clouds

OK, then what about the rule about not mixing standard and QR sprinklers in
the same space? Are above and below sprinklers with an 11" gap considered to
be the same space or separate spaces?  If the cloud was 10 ft x 10 ft in the
middle of a 30 x 30 room, would you say the same? However, there is also
something out there about calculating only one level or the other, but not
necessarily both (I believe in 13-2010, but I am far from adept with this
addition and have yet to find it). If that is the case does this overrule
the mixing ban since only one level or the other is expected to react to the
fire?


At 08:01 PM 7/12/2011, you wrote:
>Todd,
>
>I would say that since this is light hazard you should use the QR heads.
>
>Cliff Whitfield, SET
>President
>Fire Design, Inc.
>850-526-1886
> 
>
>
>[email protected]
>www.fire-design.com
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd 
>Williams
>Sent: Tuesday, July 12, 2011 5:12 PM
>To: [email protected]
>Subject: QR sprinklers and clouds
>
>I am working on a project where a cloud ceiling is being installed in 
>part of the space. The gap is 11" between the cloud and the rest of the 
>ceiling on each side. The existing sprinklers at the deck at standard 
>response. Do the sprinklers below the cloud need to be SR as well or can
the be QR?
>(Light Hazard occupancy)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to