Continuing prior posting, I do not recall ever looking for a pressure loss through a hydrant. The data may be available from the mfr, but if not, you may have to make an estimate based on the design of the hydrant valve. At the least, it will be a sharp 90 and something like a globe valve. My Crane pipe and fittings book puts a nominal 6" (my estimate of a 5-1/4 inch typical Mueller hydrant) globe valve at about 160' of pipe. Add your elbow and tee plus lead-in piping and run a Hazen Williams calc for the loss.
Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)