8.14.1.2.1 is more applicable. This section permits small openings to noncombustible concealed spaces. Many people don't realize, but in many scenarios, the return air grilles you see in the ceiling are not ducted. They are open tiles with decorative finishes leading directly to unsprinklered noncombustible concealed spaces. The question you have to ask yourself is whether or not you consider the open mesh ceiling a small opening. And, whether the small opening verbiage applies room by room or to the ceiling as a whole.
Additionally, you have to ask was the original installation installed prescriptively or as a performance based option? Probably not prescriptively. But, it appears that sprinklers where installed above the opening to the concealed space to protect the cell and for security reasons, the sprinklers were raised 5 - 6 feet. Since the cell is rather small (175 sq. ft.), the fire plume should activate the sprinklers above. From a performance based perspective, it makes sense. The other question you must ask is: are there approved as-builts on record to justify the installation?? Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: Todd Williams [mailto:[email protected]] Sent: Tuesday, July 26, 2011 11:13 AM To: [email protected] Subject: Re: Concealed Space? Could you apply NFPA 13 (2002) section 8.14.1.5? (or the newer equivalent) At 09:45 AM 7/26/2011, you wrote: >Okay here is the situation. I have a Medical/Dental Facility which is part >of a prison complex. The building is a noncombustible Butler type building >approx. 6,200 sq. ft. in area. Ceilings are a combination of suspended >ceiling tile and drywall. Walls are metal studs and drywall. Pretty >straightforward so far. However they have a Detainee Holding Cell which is >approx. 175 sq. ft. in area with a mesh type ceiling (almost like heavy >duty chain link fence) above. From inside the cell you can look up and see >the roof deck above. The walls around the cell are concrete block and only >extend about 6" above the ceiling area of the adjacent rooms. This is a >holding cell only, no bed, etc. Inmates wait in this cell before being >removed for examination. Sprinkler protection is installed throughout the >entire drop ceiling area. No sprinkler protection at the roof deck above >except for two heads over the cell. Heads are about 5'-6' above cell. Is >this acceptable? Is this space still considered a noncombustible concealed >space not requiring sprinkler protection throughout? My thinking is that >for this to be acceptable the walls around the cell should extend to the >roof deck. > >Matt >Matthew Drewello, P.E. l FLUOR l Senior Design Engineer - Fire Protection >l [email protected] l O +864.517.1814 l www.fluor.com >------------------------------------------------------------ >The information transmitted is intended only for the person >or entity to which it is addressed and may contain >proprietary, business-confidential and/or privileged material. >If you are not the intended recipient of this message you are >hereby notified that any use, review, retransmission, dissemination, >distribution, reproduction or any action taken in reliance upon >this message is prohibited. If you received this in error, please >contact the sender and delete the material from any computer. > >Any views expressed in this message are those of the individual >sender and may not necessarily reflect the views of the company. >------------------------------------------------------------ >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
