I would suggest that the insurance company give you some idea of what the insurance company is looking for. Back in the old days the insurance company that I work for use to have engineering guides for such opening protective water spray systems for conveyors or other material handling systems when required to penetrate fire walls, and fire doors are not feasible. The opening must be protected on both sides of the wall by a deluge water spray tunnel system in accordance with (I think)FM Global Data Sheet 1-23, Protection of Openings in Fire Subdivisions. The deluge water spray tunnel system must consist of a separate water spray system for both sides of the opening, and a metal or masonry enclosure around the opening extending a minimum of 1.5 m (5 ft) from both sides of the wall. The spray system must consist of open spray nozzles that provide a minimum of 1.356 L/s per m2 (2.0 gpm/ft2) of opening and must be activated by heat detectors. Any detector must activate both systems simultaneously. The systems must be supplied from a separate riser independent of the overhead sprinkler system. Each system must be equipped with a control valve. The water supply must be capable of supplying the deluge systems in addition to other required fire protection demands. Operation of any deluge system or sprinkler system protecting the area of the handling system must automatically shut down the handling system. This is from the memory of an "old" guy might need to check the FM Data sheet number.
Have a fire safe day. Jim Davidson Davidson Associates Fire Protection * Medical Gas * Code Consulting 302-994-9500 Fax:302-234-1781 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, August 03, 2011 12:15 PM To: [email protected] Subject: Re: Unprotected Opening This recommendation came from somewhere (ie insurance company). Find the source and start asking there. At 11:39 AM 8/3/2011, you wrote: >We have an industrial project with a 3hr firewall separating two areas. On >one side of the fire wall has no protection at the roof per its industrial >rating and on the other side is a paint area protected as EH GroupII >(.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product >passes through from one side to the other. We are being asked to put >sprinklers on the non protected side of the opening supplied by a deluge >system. Apparently I am overlooking the requirements (spacing, density, >etc.); where would I find these requirements or would I simply use the >requirements of the protected side - .40/2500 spaced at max 12'-0? > > > >Thank you, > > > >Bobby Gillett > >Sr. Project Manager > >Key Fire Protection, Inc. > >(731) 424-0130 office (731) 424-9285 fax > >(731) 267-4853 cell > > <mailto:[email protected]> >[email protected] > > > > > > > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)