I would suggest that the insurance company give you some idea of what the 
insurance company is looking for. Back in the old days the insurance company 
that I work for use to have engineering guides for such opening protective 
water spray systems for conveyors or other material handling systems when 
required to penetrate fire walls, and fire doors are not feasible. The opening 
must be protected on both sides of the wall by a deluge water spray tunnel 
system in accordance with (I think)FM Global Data Sheet 1-23, Protection of 
Openings in Fire Subdivisions. The deluge water spray tunnel system must 
consist of a separate water spray system for both sides of the opening, and a 
metal or masonry enclosure around the opening extending a minimum of 1.5 m (5 
ft) from both sides of the wall. The spray system must consist of open spray 
nozzles that provide a minimum of 1.356 L/s per m2 (2.0 gpm/ft2) of opening and 
must be activated by heat detectors. Any detector must activate both systems 
simultaneously. The systems must be supplied from a separate riser independent 
of the overhead sprinkler system. Each system must be equipped with a control 
valve. The water supply must be capable of supplying the deluge systems in 
addition to other required fire protection demands. Operation of any deluge 
system or sprinkler system protecting the area of the handling system must 
automatically shut down the handling system. This is from the memory of an 
"old" guy might need to check the FM Data sheet number.

Have a fire safe day.

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, August 03, 2011 12:15 PM
To: [email protected]
Subject: Re: Unprotected Opening

This recommendation came from somewhere (ie insurance company). Find the source 
and start asking there. 


At 11:39 AM 8/3/2011, you wrote:
>We have an industrial project with a 3hr firewall separating two areas. On
>one side of the fire wall has no protection at the roof per its industrial
>rating and on the other side is a paint area protected as EH GroupII
>(.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product
>passes through from one side to the other. We are being asked to put
>sprinklers on the non protected side of the opening supplied by a deluge
>system. Apparently I am overlooking the requirements (spacing, density,
>etc.); where would I find these requirements or would I simply use the
>requirements of the protected side - .40/2500 spaced at max 12'-0?
>
> 
>
>Thank you,
>
> 
>
>Bobby Gillett
>
>Sr. Project Manager
>
>Key Fire Protection, Inc.
>
>(731) 424-0130 office  (731) 424-9285 fax 
>
>(731) 267-4853 cell
>
> <mailto:[email protected]>
>[email protected]
>
> 
>
> 
>
> 
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to