Craig,

I'll buy. Not too many smokestacks in NW any more and so my industrial
experience is limited. Enjoy the rest of the day.

On Wed, Aug 3, 2011 at 9:48 AM, <[email protected]> wrote:

> Ron, I'd agree with you if the areas were not physically separated by a
> rated fire wall.  But since they are, I would not apply the 15ft rule.
>
> In industrial sites where there are product conveyors passing through rated
> walls it is common for a physical break in the conveyor system at the wall
> with a rated fire door tied into a sensing and release system with
> electronic stop commands tied into the conveyor.  Sensors are installed to
> determine the product is not in position to hinder fire door closures and
> bump the conveyor to clear the opening, smoke or heat detection is often
> employed on both sides of the opening to start this whole shut down process.
> This is all automatic and happens in seconds.
>
> There are some provisions within the FM data sheets specifically 1-23 where
> spray sprinklers are shown as a means to protect small openings.  However,
> is says specifically SMALL openings and it doesn't give any criteria for the
> discharge being equal to a specific hour-rating.  The majority of the text
> within 1-23 calls for listed door assemblies at rated openings.
>
>
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Wednesday, August 03, 2011 12:00 PM
> To: [email protected]
> Subject: Re: Unprotected Opening
>
> I'd say you protect per the rule that requires the higher demand area
> extend
> fifteen feet into the lesser demand area. I'd suggest that this means
> fifteen feet straight through the opening and fifteen feet to either side.
> This is in 13 and you'll need to find it per your in use edition. That
> would
> be normal for two hazards in one building. You could also look under
> "Exposure Protection" which provides guidelines for buildings too close
> together with openings but this seems to me to apply only between
> properties, not within buildings themselves. Finally there are the "holes
> through the floor" layouts for things like escalators but I don't think
> that's applicable.
>
> On Wed, Aug 3, 2011 at 8:39 AM, Bobby Gillett <
> [email protected]> wrote:
>
> > We have an industrial project with a 3hr firewall separating two areas.
> On
> > one side of the fire wall has no protection at the roof per its
> industrial
> > rating and on the other side is a paint area protected as EH GroupII
> > (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product
> > passes through from one side to the other. We are being asked to put
> > sprinklers on the non protected side of the opening supplied by a deluge
> > system. Apparently I am overlooking the requirements (spacing, density,
> > etc.); where would I find these requirements or would I simply use the
> > requirements of the protected side - .40/2500 spaced at max 12'-0?
> >
> >
> >
> > Thank you,
> >
> >
> >
> > Bobby Gillett
> >
> > Sr. Project Manager
> >
> > Key Fire Protection, Inc.
> >
> > (731) 424-0130 office  (731) 424-9285 fax
> >
> > (731) 267-4853 cell
> >
> >  <mailto:[email protected]>
> > [email protected]
> >
> >
> >
> >
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to