Craig, I'll buy. Not too many smokestacks in NW any more and so my industrial experience is limited. Enjoy the rest of the day.
On Wed, Aug 3, 2011 at 9:48 AM, <[email protected]> wrote: > Ron, I'd agree with you if the areas were not physically separated by a > rated fire wall. But since they are, I would not apply the 15ft rule. > > In industrial sites where there are product conveyors passing through rated > walls it is common for a physical break in the conveyor system at the wall > with a rated fire door tied into a sensing and release system with > electronic stop commands tied into the conveyor. Sensors are installed to > determine the product is not in position to hinder fire door closures and > bump the conveyor to clear the opening, smoke or heat detection is often > employed on both sides of the opening to start this whole shut down process. > This is all automatic and happens in seconds. > > There are some provisions within the FM data sheets specifically 1-23 where > spray sprinklers are shown as a means to protect small openings. However, > is says specifically SMALL openings and it doesn't give any criteria for the > discharge being equal to a specific hour-rating. The majority of the text > within 1-23 calls for listed door assemblies at rated openings. > > > > Craig L. Prahl, CET > Fire Protection > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Ron Greenman > Sent: Wednesday, August 03, 2011 12:00 PM > To: [email protected] > Subject: Re: Unprotected Opening > > I'd say you protect per the rule that requires the higher demand area > extend > fifteen feet into the lesser demand area. I'd suggest that this means > fifteen feet straight through the opening and fifteen feet to either side. > This is in 13 and you'll need to find it per your in use edition. That > would > be normal for two hazards in one building. You could also look under > "Exposure Protection" which provides guidelines for buildings too close > together with openings but this seems to me to apply only between > properties, not within buildings themselves. Finally there are the "holes > through the floor" layouts for things like escalators but I don't think > that's applicable. > > On Wed, Aug 3, 2011 at 8:39 AM, Bobby Gillett < > [email protected]> wrote: > > > We have an industrial project with a 3hr firewall separating two areas. > On > > one side of the fire wall has no protection at the roof per its > industrial > > rating and on the other side is a paint area protected as EH GroupII > > (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) where product > > passes through from one side to the other. We are being asked to put > > sprinklers on the non protected side of the opening supplied by a deluge > > system. Apparently I am overlooking the requirements (spacing, density, > > etc.); where would I find these requirements or would I simply use the > > requirements of the protected side - .40/2500 spaced at max 12'-0? > > > > > > > > Thank you, > > > > > > > > Bobby Gillett > > > > Sr. Project Manager > > > > Key Fire Protection, Inc. > > > > (731) 424-0130 office (731) 424-9285 fax > > > > (731) 267-4853 cell > > > > <mailto:[email protected]> > > [email protected] > > > > > > > > > > > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > For Technical Assistance, send an email to: [email protected] > > > > To Unsubscribe, send an email > to:[email protected] > > (Put the word unsubscribe in the subject field) > > > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering Technology > Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA 98405 > > [email protected] > > http://www.bates.ctc.edu/fireprotection/ > > 253.680.7346 > 253.576.9700 (cell) > > Member: > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC > > They are happy men whose natures sort with their vocations. -Francis Bacon, > essayist, philosopher, and statesman (1561-1626) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)