Fire Protection System Inspection FM 2-81 (January 2008), Page 32 contains a specific requirement.

Joint Commission also had a requirement. I concur with the Top as well, if there is evidence of past freeze ups, evidence of sprinkler service work performed by others, work in the area by other trades (e.g. HVAC install or replacement), or evidence of mechanical impact damage (e.g. parking garages) then recommendation to the client to check pitch should be made.

Byron


-----Original Message----- From: Ron Greenman
Sent: Thursday, August 25, 2011 7:47 PM
To: [email protected]
Subject: Re: Dry Pipe System Pitch Inspection

Seems to me there was a line in the old 13A that ran something like, "Dry
pipe system checked for pitch?" All my old stuff is at work and I'm at home
so can't look it up.

On Thu, Aug 25, 2011 at 12:49 PM, George Church <[email protected]>wrote:

We've seen some "abbreviated" ITM forms used by a competitor and we're no
longer wondering why he beats us- he doesn't do half the work.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] [mailto:
[email protected]] On Behalf Of David de Vries
Sent: Thursday, August 25, 2011 2:51 PM
To: [email protected]
Subject: RE: Dry Pipe System Pitch Inspection

Thanks, Top.  You are quite right that pitch is something that goes to the
original installation.  I was pretty sure it was not in 25 after looking
thru the current and 08 editions.

I did hear off-forum that there was such a line item in an old inspection
form used by some contractors. That is apparently where I got the notion of
such a requirement.

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated


--- On Wed, 8/24/11, Top Myers <[email protected]> wrote:


From: Top Myers <[email protected]>
Subject: RE: Dry Pipe System Pitch Inspection
To: [email protected]
Date: Wednesday, August 24, 2011, 9:38 PM


There is no requirement to check pitch in NFPA-25. It is assumed that
system was properly installed.  I would suggest if you feel there has been
building settlement or some other reason you feel there may be a problem it
makes sense to check but this would be outside scope of 25 inspection and
should be qualified as such.

Top Myers
Myers Risk Services
PO Box 741
Kimberton, PA 19442
O - 484-924-8155  C - 610-952-0965
[email protected]

Providing Solutions For Your Risk Management  Needs


-----Original Message-----
From: [email protected] [mailto:
[email protected]] On Behalf Of David de Vries
Sent: Wednesday, August 24, 2011 6:01 PM
To: AFSA SprinklerForum
Subject: Dry Pipe System Pitch Inspection

Somewhere I remember seeing a requirement that the pitch of dry pipe
systems must be periodically checked, like at a 5 year or 10 year interval. When I went looking for it in 25, I could not find it. Did I imagine this,
or is it actually out there somewhere?

Thanks.

Dave

David A. de Vries, P.E., CSP
Firetech Engineering Incorporated

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110824/0aaaaf20/attachment.html
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110825/c750b8fc/attachment.html
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110825/9559cbda/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to