Is there an error in Table 17.3.3.1?

I notice in exposed unexpanded 35ft storage in 40ft building section there
is a big penalty for using 25.2k sprinklers.

14.0k at 75psi ~ 121gpm

16.8k at 52psi ~ 121gpm

25.2k at 50psi ~ 178gpm

 

For the same heights with cartoned unexpanded, the numbers are the same with
the exception of 25psi for the 25.2k.

 

I checked the errata for NFPA 13 2010ed and didn't see anything. 

 