Is there an error in Table 17.3.3.1? I notice in exposed unexpanded 35ft storage in 40ft building section there is a big penalty for using 25.2k sprinklers.
14.0k at 75psi ~ 121gpm 16.8k at 52psi ~ 121gpm 25.2k at 50psi ~ 178gpm For the same heights with cartoned unexpanded, the numbers are the same with the exception of 25psi for the 25.2k. I checked the errata for NFPA 13 2010ed and didn't see anything. Randy Knutson, CET Sales Manager Shilo Automatic Sprinkler, Inc. (208) 412-6113 cell (208) 466-0006 ext 119 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110912/fcff7a3d/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum