Thanks Jeff. I saw some earlier errata on the ESFR tables and this looked skewed to me. I went and looked through the FM Global data sheets and it made somewhat more sense to me.
Randy Knutson Shilo Automatic Sprinkler, Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeff Hewitt, PE Sent: Monday, September 12, 2011 2:34 PM To: [email protected] Subject: RE: Table 17.3.3.1 ESFR Protection Randy, There is no error. Not all ESFR are created equal. K25 and K22 will not protect the same things that K14 and K17 will. Jeff Hewitt, PE, SET Corporate Engineer BI-STATE FIRE PROTECTION C O R P O R A T I O N 636-946-0011 office 636-946-5172 fax 314-574-6989 cell Fire Sprinklers save lives. Can you live without them? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Randy Knutson Sent: Monday, September 12, 2011 3:31 PM To: [email protected] Subject: Table 17.3.3.1 ESFR Protection Is there an error in Table 17.3.3.1? I notice in exposed unexpanded 35ft storage in 40ft building section there is a big penalty for using 25.2k sprinklers. 14.0k at 75psi ~ 121gpm 16.8k at 52psi ~ 121gpm 25.2k at 50psi ~ 178gpm For the same heights with cartoned unexpanded, the numbers are the same with the exception of 25psi for the 25.2k. I checked the errata for NFPA 13 2010ed and didn't see anything. Randy Knutson, CET Sales Manager Shilo Automatic Sprinkler, Inc. (208) 412-6113 cell (208) 466-0006 ext 119 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20110912/fcff7a3d/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum