Tom, A Hose Monster is really no different than the standard play-pipe arrangement except that the pito(s) are fixed in the device so yo don't have to hand hold the devices against the stream and they are so configured that reactive forces are balanced so the hoses and nozzles don't go whipping about. Just a more convenient tool.
On Mon, Sep 26, 2011 at 6:01 AM, Tom Binkley <[email protected]>wrote: > Thanks George, > Over here we do not have "Hose Monster" (to my knowledge) although I have > had a look and understand that it measures pressure and full flow on single > or multiple connections. > I will look into this piece of kit a bit further now that I am aware of the > who and what. > > For the posed question are we right to think there are distinct stages? > > 1) Check the pump has the closed head pressure that was there at the > handover. > > 2) If we are testing at the common pipe location we think we will need to > know by way of written hydraulic calculations exactly what pressure and flow > is anticipated at the location. > > 3) If we are testing at the end of the line, then we propose that 'to be > correct', they both need to be tested concurrently so that the sum of both, > equals the design criteria requirements and the readings should be below > (because you have more than requirements) or at least on the pump curve > line. > We agree with you and it is worth emphasis that the pressure at the common > pipe prior to the split for roof and rack is very important information, in > that it enabled the balancing calculations that were carried out and can > also be subsequently validated. > > 4) Dropping the flow off for system 1 and then measuring the flow at system > 2, we think this is a balancing act because as you open up system 2 it will > change what is happening at the pre-set system 1, which will create > iterative testing as one adjustment after another impacts on the combined > systems pressures and flows. > > Has anyone actually concurrently tested a dual system (1 and 2)? > > A further thought; to do this inside warehouses using "Hose Monster" seems > to be an impractical proposition having due regard for: > a) Hoses should be short > b) The expulsion of large volumes of water > c) It must be cost effective'. > > Regards > Tom > > -----Original Message----- > From: George Church [mailto:[email protected]] > Sent: 20 September 2011 13:32 > To: [email protected] > Subject: RE: Design criteria check > > If you're asking why I think you're asking, it may require two separate > flows, one at the end of the in-racks, one at the end of the roof system. > Throttle flows to balance and replicate the design flows against each other, > and you'd have the "bucket test" for a commercial application I think you're > seeking. > > Could also go back to the split, if there's not a separate riser, and do a > combined flow, but that wouldn't provide the end of line verification. If > they are separate risers, you could drop the flow off system 1 and do end of > line verification off system 2; then switch. Only one flowmeter needed in > this arrangement, main drain flow via pitot or hose monster, verification of > residual at base of riser pressure gauge. > > I've only had a half up of java, so verify I'm correct! > > > George L. Church, Jr., CET > Rowe Sprinkler Systems, Inc. > PO Box 407, Middleburg, PA 17842 > 877-324-ROWE 570-837-6335 fax > [email protected] > > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Tom Binkley > Sent: Tuesday, September 20, 2011 5:54 AM > To: [email protected] > Subject: Design criteria check > > When a fire pump is designed for roof and in rack protection (operating > together) how can the end of line design criteria be verified? Has anyone > ever done this? > > Regards > > > > Tom Binkley > > Development Engineer > > ProjectFire > > t: +44 (0)1889 270999 ext.123 > > f: +44 (0)1889 272735 > > e: [email protected] <mailto:[email protected]> > > > w: www.projectfire.co.uk <http://www.projectfire.co.uk> > > > > Pasturefields Industrial Estate, Pasturefields Lane > > Hixon, Staffordshire, ST18 0PH, UK > > > > PFP Ltd Company Reg. # 3648507 VAT # 715507741 > > PFE Ltd Company Reg. # 1258677 VAT # 280452174 > > > > Information contained within this email is intended for the use of the > addressee only. If you are not the intended recipient and you have received > this email in error then any use, dissemination, distribution, or copying of > this email is strictly prohibited and you should contact the sender by email > return and then delete all the material from your system. Any views or > opinions presented within the email are solely those of the author and do > not represent those of Project Fire. This email does not form part of a > legally binding agreement. If there is an attachment with this document: The > contents of this email attachment may contain software viruses that could > damage your own computer system. > Whilst we have taken every reasonable precaution to minimize this risk we > cannot accept liability for any damage, which you sustain as a result of > software viruses. You should therefore carryout your own virus checks before > opening the attachment. > > > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110920/ed864821/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110926/dfb2c9b2/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum