Why not? It's more exact than generic average in the prescriptive document.
But is the difference, even across all the fittings within the design area,
to actually be significant to the operation of the a system beset with
the vagaries of reality rather than theory?

On Thu, Oct 6, 2011 at 11:02 AM, Rahe Loftin (7PCE) <[email protected]>wrote:

> I would like an opinion as to the use of the equivalent feet of pipe in
> NFPA
> 13 versus the equivalent length of pipe provided by a manufacturer for
> fittings.  For example, is it in accordance with NFPA 13 to use the
> manufacturer's equivalent feet of pipe for a roll grooved elbow fitting
> instead of the NFPA 13 requirement to use the equivalent feet for a long
> turn elbow.
>
> Rahe Loftin, PE
> Fire Protection Engineer (AHJ)
> Design & Construction 7PCE
>
> 817-371-3102
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111006/05450574/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111006/43c6d71b/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to