Thank you all.  The code language "as appropriate" was the interesting part.
 What is appropriate can be different depending on which side of the fence
you are on.  In government work, we have language that indicates that the
more stringent will apply.  I did not really want to apply this to hydraulic
calculations, but am having issues getting a contractor to meet the minimums
set out in the specifications and codes.

Rahe Loftin, PE
Fire Protection Engineer (AHJ)
Design & Construction 7PCE

817-371-3102



On Thu, Oct 6, 2011 at 1:23 PM, Sprinkler Academy - C Bilbo <
[email protected]> wrote:

>
> I am not sure what Professor Greenman said (I don't think I know what
> "vagaries" are....)  :-P
>
> but I think I agree with with him if he is saying that you are most
> certainly allowed to use the "hydraulic equivalent length" from a
> manufacturer's chart.  NFPA 13 Chapter 22.4.3.1.1 says, "Table 22.4.3.1.1
> shall be used to determine the equivalent length of pipe for fittings and
> devices unless manufacturer’s test data indicate that other factors are
> appropriate."
>
> So, if a manufacturer includes this data in their material data sheets,
> then it is appropriate to use that information when performing calculations.
>
> It should be recognized that the above is my opinion as a member of the
> NFPA 13 Installation Criteria Committee, and has not been processed as a
> formal interpretation in accordance with the NFPA Regulations Governing
> Committee Projects and should therefore not be considered, nor relied upon,
> as the official position of the AFSA, NFSA, NFPA, nor any of their technical
> committees.
>
> Sincerely,
>
>
> Cecil Bilbo
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217.607.0325
> www.sprinkleracademy.com
> [email protected]
>
>
> OUR STUDENTS SAVE LIVES!!
>
>
>
> ----------------------------------------
> > Date: Thu, 6 Oct 2011 11:10:00 -0700
> > Subject: Re: Manufacturer's Fittings
> > From: [email protected]
> > To: [email protected]
> >
> > Why not? It's more exact than generic average in the prescriptive
> document.
> > But is the difference, even across all the fittings within the design
> area,
> > to actually be significant to the operation of the a system beset with
> > the vagaries of reality rather than theory?
> >
> > On Thu, Oct 6, 2011 at 11:02 AM, Rahe Loftin (7PCE) <[email protected]
> >wrote:
> >
> > > I would like an opinion as to the use of the equivalent feet of pipe in
> > > NFPA
> > > 13 versus the equivalent length of pipe provided by a manufacturer for
> > > fittings. For example, is it in accordance with NFPA 13 to use the
> > > manufacturer's equivalent feet of pipe for a roll grooved elbow fitting
> > > instead of the NFPA 13 requirement to use the equivalent feet for a
> long
> > > turn elbow.
> > >
> > > Rahe Loftin, PE
> > > Fire Protection Engineer (AHJ)
> > > Design & Construction 7PCE
> > >
> > > 817-371-3102
> > > -------------- next part --------------
> > > An HTML attachment was scrubbed...
> > > URL: <
> > >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111006/05450574/attachment.html
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> > essayist, philosopher, and statesman (1561-1626)
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111006/43c6d71b/attachment.html
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111007/c9168420/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to