Here is another question for the forum. Is a jockey pump that is used, with a fire pump, for aboveground sprinkler systems acceptable to be used for a large fire pump fed underground system that supplies hydrants and buildings? It would seem that there would be more leakage underground and a 10-15 gpm jockey pump might run for an unacceptable amount of time due to underground leakage and pressure differences. This system is supplied from a ground tank that is 25 feet high.
Rahe Loftin, PE Fire Protection Engineer (AHJ) Design & Construction 7PCE 817-371-3102 -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111007/fd33e722/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum