All other things being equal except the UG leakage factor the jockey pump should not run longer per operation but will run more often. The average service life of the pump will be the same in RPMs but lessened in longevity over time. If requiring a higher pressure for the UG system than the AG, and if within the capability of the pump, then moving the cut-in/cut-out settings up and together should create no difference. If both situations exist then both answers apply.
On Fri, Oct 7, 2011 at 2:45 PM, Rahe Loftin (7PCE) <[email protected]>wrote: > Here is another question for the forum. Is a jockey pump that is used, > with > a fire pump, for aboveground sprinkler systems acceptable to be used for a > large fire pump fed underground system that supplies hydrants and > buildings? > It would seem that there would be more leakage underground and a 10-15 gpm > jockey pump might run for an unacceptable amount of time due to underground > leakage and pressure differences. This system is supplied from a ground > tank that is 25 feet high. > > Rahe Loftin, PE > Fire Protection Engineer (AHJ) > Design & Construction 7PCE > > 817-371-3102 > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111007/fd33e722/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111007/8003152b/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum