PS, Any comments on the water supply, hydraulic calculations, storage
configuration ?

John

-----Original Message-----
From: John Drucker [mailto:[email protected]] 
Sent: Tuesday, October 11, 2011 12:43 PM
To: '[email protected]'
Subject: RE: Tuesday funny

Perhaps these code sections will help;

2010 NFPA-13

7.7.1.1.3 Unless the requirements of 7.7.1.1.4 are met, a dielectric fitting
shall be installed in the junction where dissimilar piping materials are
joined (e.g., copper to steel).

7.7.1.1.4 Dielectric fittings shall not be required in the junction where
sprinklers are connected to piping.


John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd - FPDC
Sent: Tuesday, October 11, 2011 12:20 PM
To: [email protected]
Subject: Re: Tuesday funny

Send him a cut on Teflon tape. 

Sent from my iPhone

On Oct 11, 2011, at 11:58 AM, "Ed Kramer" <[email protected]> wrote:

> A client  sent this to me this morning - thought I'd share it.  This is
one
> of the comments on a plan review.  
> 
> 
> 
> "Provide means of dissimilar metal separation between galvanized steel
> piping and brass sprinkler heads ."
> 
> 
> 
> Ed Kramer
> 
> Littleton, CO
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20111011/d4502b71/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to