While I understand the frustration factor of having to go through something
like this, I disagree with John. If you can explain/teach in a civil manner
and allow the inspector to see his mistake on his own, you may very well
gain an ally on future projects. If that does not work, he always has a
supervisor (even if you have to make your way up the ladder to the State
FM). I have used both methods effectively in the past.

Mike Hill

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John O'Connor
Sent: Friday, October 14, 2011 10:16 AM
To: [email protected]
Subject: RE: How would you address this?

The problem as I see it, is an inexperienced individual with no knowledge of
what he is inspecting, has been put in a position of authority with the
power to OK or reject our work.  This is and always be unacceptable in the
eyes of good sprinkler contractors.  Is it our job to educate our overseers?
I think not.
John O'Connor
Nashville 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Smith, Steven
D. (CSFD)
Sent: Friday, October 14, 2011 8:47 AM
To: [email protected]; [email protected]
Subject: RE: How would you address this?

Quite honestly, I'm a bit disappointed with some of the responses from the
"SME's" with this forum. It's easy to poke fun at someone behind closed
doors. My guess is that most if not everyone here didn't know much more than
this inspector when they first started in the business. I sure didn't. 

Being an AHJ myself, I would personally appreciate it if a knowledgeable
contractor were to approach me with a different way of thinking. This is a
prime opportunity to create a relationship with the inspector that may help
you out in the future. Showing that the contractor cares about doing the job
right and showing how that's done could go a long way.
Then maybe a follow up phone call to his supervisor, not to get the
inspector in trouble, but to inform the supervisor of what transpired and
how it was resolved. Granted, you may have to gauge how the inspector would
receive all of this and base your actions on that. 

As I mentioned, this could be a great opportunity to show how professional
you are and the quality of your work. Especially if sprinkler companies and
AHJ's alike wish to install more of these systems in homes. Unfortunately
there are far too many contractors out there that aren't professional and
have poor quality that will make it easy for decision makers to keep
sprinklers out of homes. 

Just my 1/2 cent.

Steve Smith
Colorado Springs Fire Department

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Thursday, October 13, 2011 4:44 PM
To: [email protected]
Subject: How would you address this?

This was a first for me to day.  During an inspection of a residential
system today, the AHJ inspector would put a dot on the floor and run his

tape in a circle at the spacing limit of the heads.  He would not sign off
on the system because the heads were 8' off of each wall, but with the
radius, that leaves a "dry" spot in the corner of the room.  He did the same
thing in rooms with multiple heads.  The heads were 16' apart.

There were 4 heads in this room.  He would draw circles on the floor of an
8' radius.  Since there was not overlap of his circles, he would not pass
the system today.

Has anyone ever encountered this?  How did you address it?  This is a new
inspector and he admits that fire sprinklers are not his specialty, but he
has to do this job.

--
Please feel free to call if you have any questions or comments.

Sincerely,

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
Office (480) 505-9271
Fax (866) 430-6107

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1411 / Virus Database: 1522/3951 - Release Date: 10/14/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to