I am assuming NYC Building Code
You already have two exit enclosures on the sides so you are covered so long as your occupant load does not require three. So in the middle you probably have a stairway not required for egress. NYC BC Section 1019.1 Exception 4 says no enclosure is required when you comply with 707.2. You probably comply with 707.2 Exception number 7. There is a whole list of things like not connecting more than two stories, is not part of means egress, etc. If you don’t comply with Exception 7, Exception 2 is the one you are thinking of that requires the “water curtains” designed in accordance with NFPA 13 (as modified in Appendix Q for NYC). Since you only connect two stories, you most likely comply with 7. The code sections are roughly the same if you are just under the 2006 edition of IBC and not NYC. Later editions of IBC For information this is also found in IBC 2009 Section 708.2 -2.1 and 2.2 references NFPA 13. IBC 2012 Section 1009.3 Exception 3 and 4 is the one that referenced NFPA 13(moved out of Chapter 7 into Chapter 10) That are many other things that could come into play so use this information with caution. Hope it helps Justin Reid On Tue, Nov 15, 2011 at 2:15 PM, Steve Mackinnon <[email protected]>wrote: > When are water curtain's required? > > > > I have a two level gym with an open staircase in the middle. The floor > has two rated staircases, one either side of the floor. Am I to provide > a water curtain for the open staircase? Opening is 13 f x 10 ft. It > seams 8.15.4.4 requires me to provide one... please help. > > > > Thanks > > Steven > > > > > > Steven MacKinnon > > Senior Fire Protection Engineer > > Hartcorn Plumbing & Heating Inc. > > 850 South 2nd Street > > Ronkonkoma, NY 11779 > > 631-580-2300 - Office > > 631-580-1090 - Fax > > [email protected] > > > > > > > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: < > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111115/26ff9b42/attachment.html > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111115/ce36df35/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum