You should be. The IBC 2003 Edition references the same sections as 2006. Sections 707.2 Exception 7 referenced from 1019.1 would be the scenario where a water curtain IAW NFPA 13 would not be required.
Justin Reid On Wed, Nov 16, 2011 at 7:52 AM, Steve Mackinnon <[email protected]>wrote: > Thank you Justin for the response. Actually I'm out on Long Island and > using NFPA 13, 2007 and I think NY State references IBC 2003... (but not > 100%) > > So it seams like I'm good... > > Thanks > Steven > > > > Steven MacKinnon > Senior Fire Protection Engineer > Hartcorn Plumbing & Heating Inc. > 850 South 2nd Street > Ronkonkoma, NY 11779 > 631-580-2300 - Office > 631-580-1090 - Fax > [email protected] > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Justin > Reid > Sent: Tuesday, November 15, 2011 4:10 PM > To: [email protected] > Subject: Re: Water Curtain's > > I am assuming NYC Building Code > > > > You already have two exit enclosures on the sides so you are covered so > long as your occupant load does not require three. So in the middle you > probably have a stairway not required for egress. > > > > NYC BC Section 1019.1 Exception 4 says no enclosure is required when you > comply with 707.2. > > You probably comply with 707.2 Exception number 7. There is a whole list > of > things like not connecting more than two stories, is not part of means > egress, etc. > > > > If you don't comply with Exception 7, Exception 2 is the one you are > thinking of that requires the "water curtains" designed in accordance > with > NFPA 13 (as modified in Appendix Q for NYC). > > > > Since you only connect two stories, you most likely comply with 7. > > > > The code sections are roughly the same if you are just under the 2006 > edition of IBC and not NYC. > > > > Later editions of IBC > > For information this is also found in > > IBC 2009 Section 708.2 -2.1 and 2.2 references NFPA 13. > > IBC 2012 Section 1009.3 Exception 3 and 4 is the one that referenced > NFPA > 13(moved out of Chapter 7 into Chapter 10) > > > > That are many other things that could come into play so use this > information with caution. > > > > Hope it helps > > > > Justin Reid > > > On Tue, Nov 15, 2011 at 2:15 PM, Steve Mackinnon > <[email protected]>wrote: > > > When are water curtain's required? > > > > > > > > I have a two level gym with an open staircase in the middle. The floor > > has two rated staircases, one either side of the floor. Am I to > provide > > a water curtain for the open staircase? Opening is 13 f x 10 ft. It > > seams 8.15.4.4 requires me to provide one... please help. > > > > > > > > Thanks > > > > Steven > > > > > > > > > > > > Steven MacKinnon > > > > Senior Fire Protection Engineer > > > > Hartcorn Plumbing & Heating Inc. > > > > 850 South 2nd Street > > > > Ronkonkoma, NY 11779 > > > > 631-580-2300 - Office > > > > 631-580-1090 - Fax > > > > [email protected] > > > > > > > > > > > > > > > > -------------- next part -------------- > > An HTML attachment was scrubbed... > > URL: < > > > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachm > ents/20111115/26ff9b42/attachment.html > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach > ments/20111115/ce36df35/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111116/eec91792/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum