Schedule 40 is standard weight up through 10" pipe sizing per the Machinery's 
Handbook 26th Edition Pipe and Pipe Fittings Table 1. American National 
Standard Weights and Dimensions of Welded and Seamless Wrought Steel Pipe 
ANSI/ASME B36.10M-1995.  DoD guidelines required schedule 40 piping in many 
applications and require grooving to be cut, not rolled, something that cannot 
be done with schedule 10.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, November 29, 2011 8:46 AM
To: [email protected]
Subject: RE: STANDARD WEIGHT RISER PIPE

There is no requirement in 13 for a riser to be Schedule 40. 
The EOR must be wanting to increase the robustness of the riser for some other 
reason.
Hopefully he doesn't require threaded joints or there may be some guys looking 
for larger wrenches than they're used to using (and maybe some larger muscles 
than they have).

While some might quibble that "standard weight" could now be argued to be Sch 
10 for sprinkler mains and risers based on industry usage, I don't think they'd 
win an argument with the EOR that when he said standard weight, he meant Sch 40.

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, November 29, 2011 8:29 AM
To: [email protected]
Subject: STANDARD WEIGHT RISER PIPE

In the spec it states; "Each vertical water supply riser shall be standard 
weight pipe from grade floor level at entry of feed main into building up to 
the highest horizontal cross main."


What is that supposed to mean?  I've had more contractor confusion over that 
statement and I've been trying to find if there's a requirement for the riser 
to be Schedule 40 instead of allowing it to be Schedule 10 within the NFPA 13 
Standard.  So far I haven't found anything that dictates pipe weight for a 
riser.  

Anyone have any insight to offer?

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to