Bottom line is that NFPA 13, 20,14, and others do not use the phrase "standard 
weight" to describe fire sprinkler pipe.  Standard weight may be a phrase or 
term used in the mechanical or plumbing industries, but as we all know, fire 
sprinklers are not mechanical or plumbing.  The pipe used for fire sprinkler 
systems is specifically listed for such use and differs from other piping not 
listed for fire sprinkler use.  Furthermore, if the term standard weight is 
used in a spec for fire sprinkler piping then 13 governs.  We then would turn 
to chapter 6 and follow the standard guidelines.  An example of this might be 
hangers.  I have had engineers spec certain hanger types or assemblies that are 
permissible in plumbing and mechanical systems but are not listed for fire 
sprinkler use.  These hangers are "standard" in other industries but not 
acceptable in our industry.  Would you , as an end user use these unlisted 
assemblies?   Probably not, instead it would be properly argued that they are 
not allowed and that 13 trumps.  The same case can be made for "standard 
weight" pipe.

My two cents,

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, November 30, 2011 7:17 AM
To: [email protected]
Subject: Re: STANDARD WEIGHT RISER PIPE

"Standard Weight" is an industry "slang" and should never be used by a 
reputable Engineer in a Specification!
IMHO
Mark at Aero

----- Original Message -----
From: Ronl.Fletcher [mailto:[email protected]]
Sent: Wednesday, November 30, 2011 08:04 AM
To: [email protected] <[email protected]>
Subject: RE: STANDARD WEIGHT RISER PIPE

Agreed, standard weight is usually interpreted to be schedule 40. But couldn't 
it be said that any pipe meeting ASTM is a "standard weight"?


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, November 30, 2011 3:10 AM
To: [email protected]
Subject: RE: STANDARD WEIGHT RISER PIPE

I'll agree sch 10 is a standard weight, but not that it is "standard weight" 
pipe.
Dunno when it stopped being so, but when I was a kid, there was lightwall and 
standard weight, half and large orifice.....life was simpler and sch 40 was 
(is) standard weight.


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Timothy W Goins
Sent: Tuesday, November 29, 2011 11:31 PM
To: [email protected]
Subject: Re: STANDARD WEIGHT RISER PIPE

Sch10 is a standard weight. Dyna-flo, XL and the now not listed Sch5 are none 
standard. Maybe he just wanted to exclude the latter.

"For I am not ashamed of the gospel , , because it is God’s power for salvation 
to everyone who believes..." HCS Romans 1:16

On Nov 29, 2011, at 10:16 PM, Mark Sornsin <[email protected]> wrote:

> Maybe the engineer just stuck the term 'standard weight' in there out of 
> habit; or because his master spec has that in there; or because he thinks 
> he's doing somebody a service by requiring it.... or possibly, he has a 
> legitimate reason. Sadly, the last option is normally NOT the most likely.
> 
> Sornsin
> Ulteig
> Fargo
> ________________________________________
> From: [email protected]
> [[email protected]] on behalf of George Church 
> [[email protected]]
> Sent: Tuesday, November 29, 2011 8:45 AM
> To: [email protected]
> Subject: RE: STANDARD WEIGHT RISER PIPE
> 
> There is no requirement in 13 for a riser to be Schedule 40.
> The EOR must be wanting to increase the robustness of the riser for some 
> other reason.
> Hopefully he doesn't require threaded joints or there may be some guys 
> looking for larger wrenches than they're used to using (and maybe some larger 
> muscles than they have).
> 
> While some might quibble that "standard weight" could now be argued to be Sch 
> 10 for sprinkler mains and risers based on industry usage, I don't think 
> they'd win an argument with the EOR that when he said standard weight, he 
> meant Sch 40.
> 
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Tuesday, November 29, 2011 8:29 AM
> To: [email protected]
> Subject: STANDARD WEIGHT RISER PIPE
> 
> In the spec it states; "Each vertical water supply riser shall be standard 
> weight pipe from grade floor level at entry of feed main into building up to 
> the highest horizontal cross main."
> 
> 
> What is that supposed to mean?  I've had more contractor confusion over that 
> statement and I've been trying to find if there's a requirement for the riser 
> to be Schedule 40 instead of allowing it to be Schedule 10 within the NFPA 13 
> Standard.  So far I haven't found anything that dictates pipe weight for a 
> riser.
> 
> Anyone have any insight to offer?
> 
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1873 / Virus Database: 2102/4647 - Release Date: 11/29/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to