I just did a job where that was an issue. We used the Reliable F1 Res 49 LL 
residential sprinkler and designed using the 4" to 8" criteria.


At 02:56 PM 12/21/2011, you wrote:
>What has the forum done to run residential pendants in exposed pipe
>applications to meet the 1-4" deflector distance criteria?
>
>There doesn't seem to be a res pnd listed for more than a 4in deflector
>distance.  
>
>I have an concrete deck / beam residential application and wanted to run
>steel pipe but would need to run a 1" Bts  pipe C/L
>
>to keep the deflector within 4in.  .  I am hesitant to run CPVC with
>2-hole straps tight to the deck because of the possible stress fractures
>at the fitting/pipe joint.
>
>I guess I will go with QR sprinklers , steel pipe, and run a -8 C/L with
>uprights and calc 900 SF.
>
> 
>
> 
>
>Dewayne Martinez
>
>Design Build Fire Protection
>