What has the forum done to run residential pendants in exposed pipe
applications to meet the 1-4" deflector distance criteria?

There doesn't seem to be a res pnd listed for more than a 4in deflector
distance.  

I have an concrete deck / beam residential application and wanted to run
steel pipe but would need to run a 1" Bts  pipe C/L

to keep the deflector within 4in.  .  I am hesitant to run CPVC with
2-hole straps tight to the deck because of the possible stress fractures
at the fitting/pipe joint.

I guess I will go with QR sprinklers , steel pipe, and run a -8 C/L with
uprights and calc 900 SF.

 

 

Dewayne Martinez

Design Build Fire Protection

262-781-7900 (w)

262-781-8401 (f)

414-349-0468 (cell)

 