Todd-
If the intent of NFPA 25 and this test is to confirm the stuff actually works, 
it might be a great time to find out what the pipe scheduled standpipes will 
produce- 
Better to know soon, rather than find out when there's a fire in an 
unsprinklered area (since that's the same area where these old standpipes will 
be, Murphy's Law of Cascading Catastrophes) what the FD can expect to get out 
of these, and if they blow apart or not.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, December 29, 2011 2:59 PM
To: [email protected]
Subject: Re: NFPA 25 standpipe test

Exactly what I am dealing with. Quite honestly, if I saw something that said 
flow the most remote hose outlet, I would only flow one outlet at 250 gpm. I 
would not from that surmise that they wanted to recreate an acceptance test, if 
one was ever done. The hospital dates from at least 1912, although I don't know 
when each section was built. There was a major expansion in 2005 when they 
added a second fire pump and increase the area by about 40%.

So would the correct procedure be to go through and date each standpipe and 
figure out how each was sized. Those that are pipe schedule could be left 
alone, the pre 1993 need to be tested to 1250 gpm (partially sprinklered) and 
65 psi at the top outlet and those from 2005 tested at 1000 gpm (fully 
sprinklered) at 100 psi?

Is there anything other than handbook commentary that details exact testing 
procedures? We are using 2002 standards. 



At 10:12 AM 12/29/2011, you wrote:
>The confusion started when 25 said flow the most remote hose 
>connection.  Some focused on the fact that it used the singular tense 
>verses plural so obviously they only had to flow from ONE outlet and 
>since an outlet only has to flow 250 gpm THAT was the amount to flow 
>for the test.  DOH!
>
>Roland
>
>On Dec 29, 2011, at 6:14 AM, Todd Williams wrote:
>
>>I am working with a hospital with a total of 9 standpipes. There are 
>>standpipes that are both pre and post 1993. The original building is 
>>partially sprinklered and the new section is fully sprinklered.
>>
>>1. Is the intent of NFPA 25 that multiple standpipes be flowed 
>>simultaneously to meet the 1250 gpm demand?
>>
>>2. Should the two sections of the hospital be flow independent of each 
>>other?
>>
>>3. If yes to 1 and 2, could the new section be flowed as a fully 
>>sprinklered building (thus 1000 gpm) as opposed to 1250?
>>
>>4. How should i handle pipe schedule standpipes, if any exist?
>>
>>I haven't had to deal with 5 year standpipe tests before.
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, CT
>>860.535.2080
>>www.fpdc.com
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to