Roland,

In the Meridian One fire the PRVs were installed as required by the 1984 
edition of NFPA 14 which was the legal code at time of conversion from dry to 
wet standpipe to maintain both flowing and non-flowing pressures to a maximum 
of 100 psi. The problem was the use of pressure regulating hose nozzles which 
were incorporated into the Fire Departments high rise operations a few years 
later.      

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Friday, December 30, 2011 10:30 AM
To: [email protected]
Subject: Re: NFPA 25 standpipe test

I assume that was a result of the Meridian One fire.  To this day, the  
PRV's are listed as the prime culprit (ie in Wikipedia) instead of  
saying the city changed their equipment without addressing the older  
installed systems.  I first heard that when I talked with one of the  
chiefs that investigated the fire but that conclusion was excluded  
from the reports.  Obviously there were multiple problems but it's  
never a good idea to bring only a knife to a gun fight.

Roland


On Dec 29, 2011, at 6:43 PM, Steve Leyton wrote:

> As an example of how at least one FD has grown to address this wide  
> range of standpipe performance (sometimes in the same building),  
> City of San Franciso trucks and engines carry three different types  
> of tips.  If the ones fitting to the hose packs aren't right for a  
> particular fire, they can go all the way down to low pressure smooth  
> bore or straight stream.   But it starts with knowing what's gonna  
> come out and the signage is now a prescriptive requirement of both  
> 13 and 14, and which can be easily retrofitted.
>
> SML

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to