Read the definition of "Approved".   In a nutshell, if the AHJ is
requiring one, then it's approved.

SML



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Wednesday, February 01, 2012 9:08 AM
To: [email protected]
Subject: RE: Standpipe FDC Inlets

Steve, I'm going by what was issued by the CT State Fire Marshal. (could
not attach it. Google "Storz fire UL" . It should be the first listing).
I did not look in 14, but 13 does require the FDC to be "of an approved
type" (6.8.5 in 2002 and 6.8.3 in 2010). Unless things have changed
since this was written, there are no approved Storz connections for FDC
use. I am not aware of any. Some municipalities have ignored this in
some situations, but this is what the ruling at the state level is.


At 11:51 AM 2/1/2012, you wrote:
>Hold on there Todd.   An FDC can be approved - see 6.8.1.1 and other
>references in both 13 and 14.   If the serving FD wants an FDC
>configured a certain way because that's how they're equipped and
>programmed for firefighting operations, then by all means give the
>EXACTLY WHAT THEY WANT.  It's their connection ...
>
>SML
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd
>Williams
>Sent: Wednesday, February 01, 2012 8:45 AM
>To: [email protected]
>Subject: RE: Standpipe FDC Inlets
>
>At 11:28 AM 2/1/2012, you wrote:
>>Now, what has the forum done when the AHJ requires  a 5"X4" storz
>>connection instead?  We have only been putting one for standpipes
>>1000gpm and under.
>>Dewayne
>
>
>I tell them that since they are not UL listed for fire service, they
are
>not legal in the State of Connecticut (per State Fire Marshal)
>
>
>
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120201/ad9b2ea0/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to