Wow, where did that come from? I have never seen that before!

On Mon, Feb 13, 2012 at 3:22 PM, Dewayne Martinez <[email protected]> wrote:

> Todd,
> NFPA 13 (10ed) A8.6.5.1.2 provides some direction on this issue.
> Dewayne
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd
> Williams
> Sent: Monday, February 13, 2012 2:58 PM
> To: [email protected]
> Subject: Interior canopy obstruction
>
> I am working on a facility where they are installing some new offices in
> an industrial building. Around the perimeter of the offices is a canopy
> which extends out 2'-6" from the office walls. The canopy height is
> about 9'-6" and the ceiling sprinklers are at 18'-9". The question is do
> we need sprinklers below the canopies. Section 8.6.5.3 says that
> sprinklers need not be installed if the obstruction is less than 4'-0"
> wide. I can go along with it except in one area it covers 1/2 of a 5'-0"
> wide corridor. In that situation, I would think that sprinklers would be
> necessary. But I get the "if it's less than 4'-0"....." argument. Any
> thoughts?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120213/657cc02c/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to