Dwayne,

I tried to make the pipe chase argument with an oversized steel column 
enclosure, but was not successful. I doubt if the 55sqft would apply because it 
is horizontal enclosure as opposed to a vertical one. Are you using the 3000 
sqft remote area since you are adjacent to a combustible concealed space?



At 08:36 AM 3/8/2012, you wrote:
>I have a typical NFPA 13 designed apartment building where there are
>combustible concealed spaces created by the frame out of the tub /
>shower units.  
>
>Many of these are about 1.5SF but are more than 6in from the inside face
>of the studs.  A building inspector is asking either for sprinkler
>protection or insulation in each.
>
>I know these do not contain any pipes but why would they be any
>different that a vertical pipe chase as described in 8.15.1.2.14?  Could
>the 55sf rule of 8.15.1.2.9 be applied in these cases?
>
>Thanks,  
>
> 
>
>Dewayne Martinez
>
>Design Build Fire Protection
>