Dwayne, I tried to make the pipe chase argument with an oversized steel column enclosure, but was not successful. I doubt if the 55sqft would apply because it is horizontal enclosure as opposed to a vertical one. Are you using the 3000 sqft remote area since you are adjacent to a combustible concealed space?
At 08:36 AM 3/8/2012, you wrote: >I have a typical NFPA 13 designed apartment building where there are >combustible concealed spaces created by the frame out of the tub / >shower units. > >Many of these are about 1.5SF but are more than 6in from the inside face >of the studs. A building inspector is asking either for sprinkler >protection or insulation in each. > >I know these do not contain any pipes but why would they be any >different that a vertical pipe chase as described in 8.15.1.2.14? Could >the 55sf rule of 8.15.1.2.9 be applied in these cases? > >Thanks, > > > >Dewayne Martinez > >Design Build Fire Protection > >-------------- next part -------------- >An HTML attachment was scrubbed... >URL: ><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120308/84b51204/attachment.html> >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum