Vince, I believe that you are fine with your spacing since you are going up the slope with your 11-6½ (if I understand your description). If you space your heads 10' apart perpendicular to the slope then you have to go to a 20 psi end head condition. Just keep your heads at 8' apart and you are fine. Your spacing will end up 8 x 11-6½.
I hope this makes sense. If not, let me know and I can call you. It's very difficult for me to put into words what is easy to show with a picture or snapshot. Cliff Whitfield, SET President Fire Design, Inc. Ph: 337-261-8807 Fx: 337-261-8808 [email protected] www.fire-design.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Vince Sabolik Sent: Monday, March 12, 2012 2:11 PM To: [email protected] Subject: SLOPAGE STUFF Need some help w/ dry sprinkler spacing before I hang myself along with the pipe! Referring to Table 8.6.2.2.1 (a) - (spacing along slopes), I have this condition: Wood trusses, 36 in or less, pitching 6"/ft The "bay" is 31-0 actual, resulting in a line spacing of 10-4, or 11-6½ on that slope. My question: Does that slope dimension of 11-6½ - apply to the perpendicular dimension of 10 ft in that table? If not, can someone make sense of this? Vince Sabolik, West Tech Fire Protection, Inc. 11351 Pearl Road / Strongsville, Ohio 44136 440 238-4800 Fax 440 238-4876 ____________________________________________________________________ -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20120312/7d2a02f6/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum