THANK YOU ALL

So, what we have is this??????:

1. There's no such thing as a .10 density under a roof that's pitched at or more than 4:12

2. Spacing can be as much as 15 ft on the slope, but if it exceeds 8 ft on the flat,
        a minimum head pressure of 20 psi must be used.

3.      In no case can spacing on the flat exceed 10 ft.

Seriously, does anyone else find the table in NFPA confusing?


At 03:19 PM 3/12/2012, you wrote:
Vince,
In regard to slopeage stuff, I believe that what is being said is that the
you figure pipe length based on slopeage of pipe, but you figure coverage
area based on the flat.  Hope that helps.

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Monday, March 12, 2012 1:11 PM
To: [email protected]
Subject: SLOPAGE STUFF

Need some help w/ dry sprinkler spacing before I hang myself along with the
pipe!

Referring to Table 8.6.2.2.1 (a) - (spacing along slopes),

I have this condition:

Wood trusses, 36 in or less, pitching 6"/ft

The "bay" is 31-0 actual, resulting in a line spacing of  10-4, or 11-6½ on
that slope.

My question:

Does that slope dimension of 11-6½  - apply to the perpendicular dimension
of 10 ft in that table?

If not, can someone make sense of this?


Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio
44136       440 238-4800     Fax 440 238-4876
____________________________________________________________________


-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120312/7d2a02f6/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2114/4866 - Release Date: 03/12/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

__________ Information from ESET NOD32 Antivirus, version of virus signature database 6961 (20120312) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120312/5690dca4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to