Burton, In the 2007 edition of NFPA 72, it is Protected Premises Chapter, section 6.8.5.1.2*. In the 2010 edition it is located in 23.8.5.1.2
"For fire alarm systems employing automatic fire detectors or waterflow detection devices, at least on fire alarm box shall be provided to initiate a fire alarm signal. This fire alarm box shall be located where required by the authority having jurisdiction." Kind Regards, Tim Frankenberg Tim Frankenberg, CT, CFPS Fire Product Manager Potter Electric Signal Company LLC 5757 Phantom Drive, Ste. 125 Hazelwood, MO 63042 314-595-6900 800-325-3936 www.pottersignal.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ford, Charles Sent: Friday, March 16, 2012 11:00 AM To: [email protected] Subject: RE: Required manual stationl I clearly remember a statememt in either IBC or 72 requiring a minimun of one manual station when supervising a sprinkler system. I can't find it either code. Any suggestions? C. Burton Ford Nicet Certified NFPA Certified Fire Protection Specialist [CFPS] Cintas Fire Protection 1038 Conshohocken Road Conshohocken ,PA 19428 610-233-1400 Fax 610-233-1401 This e-mail transmission contains information that is intended to be confidential and privileged. If you receive this e-mail and you are not a named addressee you are hereby notified that you are not authorized to read, print, retain, copy or disseminate this communication without the consent of the sender and that doing so is prohibited and may be unlawful. Please reply to the message immediately by informing the sender that the message was misdirected. After replying, please delete and otherwise erase it and any attachments from your computer system. Your assistance in correcting this error is appreciated. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum