Burton,

In the 2007 edition of NFPA 72, it is Protected Premises Chapter, section 
6.8.5.1.2*. In the 2010 edition it is located in 23.8.5.1.2

"For fire alarm systems employing automatic fire detectors or waterflow 
detection devices, at least on fire alarm box shall be provided to initiate a 
fire alarm signal. This fire alarm box shall be located where required by the 
authority having jurisdiction."

Kind Regards,

Tim Frankenberg


Tim Frankenberg, CT, CFPS
Fire Product Manager
Potter Electric Signal Company LLC
5757 Phantom Drive, Ste. 125
Hazelwood, MO 63042
314-595-6900
800-325-3936
www.pottersignal.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ford, Charles
Sent: Friday, March 16, 2012 11:00 AM
To: [email protected]
Subject: RE: Required manual stationl

I clearly remember a statememt in either IBC or 72 requiring a minimun of one 
manual station when supervising a sprinkler system. I can't find it either 
code. Any suggestions?

C. Burton Ford
Nicet Certified
NFPA Certified Fire Protection Specialist [CFPS]
Cintas Fire Protection
1038 Conshohocken Road
Conshohocken ,PA 19428
610-233-1400
Fax 610-233-1401

This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


This e-mail transmission contains information that is intended to be 
confidential and privileged.  If you receive this e-mail and you are not a 
named addressee you are hereby notified that you are not authorized to read, 
print, retain, copy or disseminate this communication without the consent of 
the sender and that doing so is prohibited and may be unlawful.  Please reply 
to the message immediately by informing the sender that the message was 
misdirected.  After replying, please delete and otherwise erase it and any 
attachments from your computer system.  Your assistance in correcting this 
error is appreciated. 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to