Ron,

I'd look closely at 9.3.2.3(4), and Annex A.9.3.2.3(4), because the annex text gives some guidance, in my opinion very clear guidance, on the different intent of a building expansion joint and a seismic separation joint, as far as fire sprinkler systems are concerned.

Further, I'd review the information in Annex A.9.3.3, and the blue text in the handbook for the same section.

This is only my opinion, and doesn't reflect the official position of NFPA-13, or the Hanging and Bracing committee, or anyone else for that matter.

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]>e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website



On 3/19/2012 3:33 PM, [email protected] wrote:
Is there a physical difference in the construction of an expansion joint compared to a 
seismic joint. We have a project that has the "expansion joints" shown on the 
architectural drawings and label as such. The owner and architect are now saying that we 
have to install seismic joints every place we cross. I would like to know it there are 
any minimum clearances of other things that would differentiate the two type of 
separations.

Thanks for any input.


Ron Fletcher
Aero Automatic
Phoenix, AZ