If you are trying o get a change order I would say it is not up to us to
determine what type of joint it is. They put on the plans "expansion joint"
and you designed to it. They made a mistake or changed it to a seismic joint
now you design to that after they approve the change order. Show them that
your design based on the expansion joint was per NFPA 13 and what is
required per NFPA 13 for a seismic joint. I know they can argue, but if they
spelled out expansion joint, well enough said. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Monday, March 19, 2012 7:43 PM
To: 'John Drucker'; [email protected]
Subject: RE: Expansion Joint vs Seismic Joint

Seismic joints occur naturally when one building is built adjacent to
another, whether or not the buildings are linked
functionally. Seismic joints are also frequently introduced to separate
wings, or other parts of a single building. A
seismic joint typically creates a separation between the adjacent buildings
or parts of buildings that includes
separation of walls, floors, roof and, in the case of joints within the same
building, may also include separation, or
accommodation for movement of piping, HVAC ducts, and other elements that
have a functional need to cross the
joint. The design of seismic joints is complex and includes efforts by all
members of the design team to assure that
the joint is properly sized, adequately sealed from weather and safe to walk
on, as well as providing for adequate
movement of other systems crossing the joint and means to maintain the fire
ratings of the floor, roof and wall
systems. Joints are costly and architecturally undesirable, so they should
be incorporated with discretion.

Source: SEISMIC JOINTS IN STEEL FRAME BUILDING CONSTRUCTION 
C. MARK SAUNDERS,MSE




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2114/4881 - Release Date: 03/19/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to