Need to look at Table 16.2.1.3.2 again? Looks doable with Figure (b)
or (e) depending on if encapsulated.
Roland
On Apr 10, 2012, at 1:17 PM, Bob wrote:
I have a project with portable rack storage. The storage is a class
II
commodity to 16' The racks will be wherever ad however they want or
need at
the time. Looking at table 16.2.1.3.3.2, there appears to be no
option for
ceiling only sprinklers. Since the storage will be wherever, in-
racks are
not an option. I'm looking at ESFR's instead. There are four
options for
up to 20' storage with a 30' roof deck, I'm looking at using 25.2K
ESFR's
with the 15 psi end head pressure. Does this sound right? Have any
of you
run into this, and what have you done?
Thanks for your help,
Bob Knight, CET III
208-318-3057
www.firebyknight.com