Need to look at Table 16.2.1.3.2 again? Looks doable with Figure (b) or (e) depending on if encapsulated.

Roland


On Apr 10, 2012, at 1:17 PM, Bob wrote:

I have a project with portable rack storage. The storage is a class II commodity to 16' The racks will be wherever ad however they want or need at the time. Looking at table 16.2.1.3.3.2, there appears to be no option for ceiling only sprinklers. Since the storage will be wherever, in- racks are not an option. I'm looking at ESFR's instead. There are four options for up to 20' storage with a 30' roof deck, I'm looking at using 25.2K ESFR's with the 15 psi end head pressure. Does this sound right? Have any of you
run into this, and what have you done?

Thanks for your help,

Bob Knight, CET III
208-318-3057
www.firebyknight.com