Roland,
This table is for single and double row racks.  These portables will be used
as multi-row racks with storage deeper than 16' and aisles less than 8'.
Will table 16.2.1.3.2 still apply?  I meant to, and thought that I did,
mention the multi-row racks.   Fingers faster than brain.

Thanks,

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: Roland Huggins [mailto:[email protected]] 
Sent: Tuesday, April 10, 2012 2:52 PM
To: [email protected]; [email protected]
Subject: Re: Portable Rack Storage

Need to look at Table 16.2.1.3.2 again?  Looks doable with Figure (b) or (e)
depending on if encapsulated.

Roland


On Apr 10, 2012, at 1:17 PM, Bob wrote:

> I have a project with portable rack storage.  The storage is a class 
> II commodity to 16'  The racks will be wherever ad however they want 
> or need at the time.  Looking at table 16.2.1.3.3.2, there appears to 
> be no option for ceiling only sprinklers.  Since the storage will be 
> wherever, in- racks are not an option.  I'm looking at ESFR's instead.  
> There are four options for up to 20' storage with a 30' roof deck, I'm 
> looking at using 25.2K ESFR's with the 15 psi end head pressure.  Does 
> this sound right?  Have any of you run into this, and what have you 
> done?
>
> Thanks for your help,
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----