Roland, This table is for single and double row racks. These portables will be used as multi-row racks with storage deeper than 16' and aisles less than 8'. Will table 16.2.1.3.2 still apply? I meant to, and thought that I did, mention the multi-row racks. Fingers faster than brain.
Thanks, Bob Knight, CET III 208-318-3057 www.firebyknight.com -----Original Message----- From: Roland Huggins [mailto:[email protected]] Sent: Tuesday, April 10, 2012 2:52 PM To: [email protected]; [email protected] Subject: Re: Portable Rack Storage Need to look at Table 16.2.1.3.2 again? Looks doable with Figure (b) or (e) depending on if encapsulated. Roland On Apr 10, 2012, at 1:17 PM, Bob wrote: > I have a project with portable rack storage. The storage is a class > II commodity to 16' The racks will be wherever ad however they want > or need at the time. Looking at table 16.2.1.3.3.2, there appears to > be no option for ceiling only sprinklers. Since the storage will be > wherever, in- racks are not an option. I'm looking at ESFR's instead. > There are four options for up to 20' storage with a 30' roof deck, I'm > looking at using 25.2K ESFR's with the 15 psi end head pressure. Does > this sound right? Have any of you run into this, and what have you > done? > > Thanks for your help, > > Bob Knight, CET III > 208-318-3057 > www.firebyknight.com > > > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2012.0.1913 / Virus Database: 2411/4926 - Release Date: 04/10/12 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum