We used to call this product "Russian Rocket Fuel" as it seems to have been
developed by the Soviet Soyuz project. 
The use of Aerosol units like Pyrogen or Micro-K is OK in the enclosed
flammable liquid risks or electrical switchboard cupboards or small
electrical rooms. The small particles produced by the rapid combustion of
the chemical do leave a dusty residue which may be harmful to disc drives
and other small electronic componentry. So it would seem less suitable for
Computer Rooms etc.
The major use in NZ has been in small vessel engine rooms, flammable liquid
storage rooms and the like where dust or residue is of lesser concern.
 
With multiple canister installations the integrity and security of the
actuation firing circuits becomes an issue. These must be duplicated,
supervised and should not be run together. The first unit  that fires may
cause a circuit disconnect before later units are fired thus all units may
not discharge.

The ongoing testing and maintenance does not allow checking of the firing
device inside the container thus one can never be certain that it is going
to work. This was the same problem with pyrotechnic squib actuators but at
least you could replace them at 3 - 5 year intervals and actually fire them
all off when replacing them. Micro-K didn't use an electrical filament but
was set off by pulling a friction plug inside the chemical. This enable all
actuation components to be tested up to the friction plug connection.

I attended training courses on Pyrogen when it first came out, but have
always been concerned that it can be over sold and used in unsuitable
applications because of the cheaper initial cost.

Kind Regards,
Russell

Russell Gregory Ph  03 338 4853
Christchurch, New Zealand
e-mail [email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Nicky
Marshall
Sent: Friday, 13 April 2012 11:39 AM
To: [email protected]
Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents

I have been looking into Aerosol systems lately so that we can advise
clients if these are suitable for their use.

As mentioned below NFPA 2010 does cover the 'system' and multiple aerosol
units can cover reasonable size rooms.  
I still have concerns about the dust/particles and it is my opinion that
this is not a replacement for gaseous systems.  Suppliers advise the
particles are not of concern but there is also advice that it is not
suitable for applications such as tape storage arrays.

I have come to a conclusion of sorts that this is a cheaper option for those
wanting to protect information rather than equipment.
A full system with alarms and warning would be preferred (as per NFPA 2010),
but even cheaper still is just the aerosol unit with no alarms which is
obviously a significantly cheaper option.  But with no monitoring and
alarms, if no one knows the units have discharged in an unmanned room - what
is being achieved?  Air handling remains on and the extinguishing capacity
reduced ....

If I was recommending to a client, it would be gaseous system, aerosol
system, aerosol units.  In that order - decreasing cost gives decreasing
protection and benefits. Not to say that aerosol is less effective in fire
suppression as I have not been able to find that type of information. 

Regarding the comment about large companies not producing this type of
product,  it also made me more wary of the product.  However I do note that
Ansul/Tyco used to produce an Aerosol known as Micro-K.  Not sure what
happened to it.  Maybe someone else on the forum could comment on this?


Kind regards


Nicky Marshall
Branch Manager (Blenheim)

Protech Design
Specialist Fire Protection Consultants
03 579 5577
021 433 488
skype: nicky-marshall
105A Alabama Rd, Redwoodtown, Blenheim 7201, New Zealand PO Box 4022,
Redwood Village, Blenheim 7242, New Zealand


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Friday, 13 April 2012 1:10 a.m.
To: [email protected]
Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents

Reza my friend haven't heard from you in a long while,  E-mail me off the
forum.

NFPA 2010 addresses aerosol fire extinguishing systems.  It would seem
however that the NFPA 2010 systems are a bit different than what Firepro and
the others you mentioned are offering.

Firepro is actually UL Listed for use in the US and approved for use by
other international governing agencies.   The technology has actually been
around for more than 30 years so it's not new.

The market for aerosol may be small so if there are not substantial sales
the big companies who are already invested in other means of extinguishment
probably will leave it for someone else.  It's not a matter of them not
"approving" aerosol since they can't approve of an item, they can only
choose to offer a similar item or not.

I would agree that the aerosol extinguishing has its place in small
enclosures and such.   But cost and practicality for larger volumes would
have to be analyzed.


Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Reza Esmaeili
Sent: Thursday, April 12, 2012 8:30 AM
To: [email protected]
Subject: Aerosol vs Halocarbon/Inert extinguishing agents

Hi all,
Some companies are persuading the end users to use condensed aerosol fire
suppression systems instead of  Halocarbon/Inert extinguishing agents for
local application or total flooding protection.
I have seen many end users buying aerosol systems for server rooms/archive
rooms and don't use any other kind of protections.
 
The big companies like Tyco, Kidde, Fike & Chemetron are not offering
aerosol systems and usually say it is not a good  and even toxic! they
say halocarbon/Inert extinguishing agents are the only choice.
 
Aerosol manufactures are usually Asian companies like www.pyrogen.com.my 
(Malaysia)or www.firepro.info (Cyprus) www.granit-salamandra.ru (Russia)
with even UL listed products.
Aerosol manufactures say this a new technology and much better than others,
they say the big companies like Tyco, Kidde, Fike & Chemetron have already
invested too much on halocarbon/Inert extinguishing agents and that's why
they are not approving aerosol systems.
 
I personally think aerosol fire extinguishing generators are good for some
small spaces like electrical cabinets, but they can't be used as a total
flooding solution instead of FM-200 system in a server room as they can't
penetrate everywhere like FM-200 and also they are not clean that much.
 
Thanks for sharing your valuable experience & professional comments.
Reza
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120412/9fff7bda/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to