Burton

We're all suffering from that !

Best

Stewart
On 16 Apr 2012, at 13:58, Ford, Charles wrote:

> I did mean methyl bromide. Methly chloride burns! Note to self check memory 
> for accuracy
> 
> C. Burton Ford
> Nicet Certified
> Special Hazards IV
> Fire alarm IV
> Sprinkler III
> Water Based Inspections I
> NFPA Certified Fire Protection Specialist [CFPS]
> Cintas Fire Protection
> 1038 Conshohocken Road
> Conshohocken ,PA 19428
> 610-233-1400
> Fax 610-233-1401
> ________________________________________
> From: [email protected] 
> [[email protected]] On Behalf Of Stewart Kidd 
> [[email protected]]
> Sent: Friday, April 13, 2012 4:06 PM
> To: [email protected]
> Subject: Re: Aerosol vs Halocarbon/Inert extinguishing agents
> 
> I have done some literature research on these systems over the years, first 
> for the protection of the car shuttles on Eurotunnel and more recently when 
> one of my clients was being bounced into using them for a small power 
> generation facility in Ukraine.
> 
> Aerosol systems were developed in the 1970's in the USSR and Israel for the 
> protection of the engine compartments of armoured fighting vehicles 
> ('tanks').  There is quite a lot of research indicating that the systems 
> (when they operate) do extinguish or suppress liquid fires. One of their 
> claimed strengths is a very low maintenance burden. But there is at least 
> anecdotal evidence to suggest that their failure rate is higher than that for 
> other fire protection systems.
> 
> I've now rejected them on several occasions because:
> 
> 1. I have real problems approving a fire protection system which relies on an 
> explosive device to generate a fire fighting agent.
> 2. There are significant contamination and clean up issues. (I handled a case 
> a few years ago when the wilful discharge of a simple 6kg dry chemical 
> extinguisher in a church resulted in clean-up costs of more than $500,000.)
> 3. There are life safety issues for areas which may be occupied from time to 
> time.
> 4. I've yet to find an insurer who is comfortable with their use.
> 
> I really don't believe these things provide anything which is not done better 
> by the inert gases or the newer chemical agents such as Halotron.  (Don't get 
> me started on FM 200 and its corrosive by products).
> 
> I'll fully support Burton's sentiments if he'll add Methyl Bromide !
> 
> Stewart Kidd
> Loss Prevention Consultancy Ltd - in his personal capacity
> On 13 Apr 2012, at 20:08, Ford, Charles wrote:
> 
>> Why are we trying to compare aerosol to Halon? ( 1301, I presume not the 
>> more toxix 1211 or 2402).
>> If we must consider a dirty agent, compare it to dry chemical, say ABC.
>> The Ansul  I-101 book shows UL listing for total flood as low as 64 gm 
>> /cubic meter. Is that really relevant?
>> What is the UL listing for aerosols?
>> Total flooding hazard for DC need not be airtight either.
>> If I were selling aerosol protection, I might be convinced to remain within 
>> the space for a sales movie, but our customers like to look at the MSDS 
>> before exposing their employees to any chemical. I doubt any particulate 
>> agent would pass muster for inhalation.
>> In addition, virtually every Special Hazard system has :
>> Manual release
>> Aubible/ visual alarms
>> Time delays for evacuation
>> Automatic shutdown of processes and or air handiling.
>> Detection is always custom tailored to fit specific hazards and the expected 
>> fire devlopment and often fairly expensive.
>> 
>> IMHO, until tested, listed and accepted,  aerosols belong in the same museum 
>> with carbontetrachloride balls, Methyl Chloride spheres, ABC/Halon 1211 
>> balls and assorted dry chemical tanks with sprinkler heads attached.
>> 
>> Call me fuddy duddy
>> 
>> 
>> C. Burton Ford
>> Nicet Certified
>> Special Hazards IV
>> Fire alarm IV
>> Sprinkler III
>> Water Based Inspections I
>> NFPA Certified Fire Protection Specialist [CFPS]
>> Cintas Fire Protection
>> 1038 Conshohocken Road
>> Conshohocken ,PA 19428
>> 610-233-1400
>> Fax 610-233-1401
>> ________________________________________
>> From: [email protected] 
>> [[email protected]] On Behalf Of Reza Esmaeili 
>> [[email protected]]
>> Sent: Friday, April 13, 2012 1:40 PM
>> To: [email protected]
>> Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents
>> 
>> Thanks for the replies,
>> Look at a video showing the release of Aerosol unit while people are 
>> breathing normally.
>> http://www.aerohub.com.my/safe-to-human.html
>> 
>> They claim to be three times more effective than halon and need only 
>> 100gr/cubic meter.
>> 
>> Considering the same fire alarm system, while using aerosol instead of  
>> Halocarbon/Inert agents will save about 30% , so can I offer for normally 
>> unoccupied areas such as pump rooms, flammable liquid storage, book storage 
>> rooms, ...
>> 
>> I am not sure if aerosol units like Pyrogen have the same level of 
>> protection and reliability like FM-200, what do you think?
>> 
>> Best,
>> Reza
>> Sarian System Novin Co., Ltd.
>> www.sarian.ir
>> 
>> 
>> --- On Fri, 4/13/12, Russell & Carol Gregory <[email protected]> wrote:
>> 
>> 
>> From: Russell & Carol Gregory <[email protected]>
>> Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents
>> To: [email protected]
>> Date: Friday, April 13, 2012, 8:06 AM
>> 
>> 
>> We used to call this product "Russian Rocket Fuel" as it seems to have been
>> developed by the Soviet Soyuz project.
>> The use of Aerosol units like Pyrogen or Micro-K is OK in the enclosed
>> flammable liquid risks or electrical switchboard cupboards or small
>> electrical rooms. The small particles produced by the rapid combustion of
>> the chemical do leave a dusty residue which may be harmful to disc drives
>> and other small electronic componentry. So it would seem less suitable for
>> Computer Rooms etc.
>> The major use in NZ has been in small vessel engine rooms, flammable liquid
>> storage rooms and the like where dust or residue is of lesser concern.
>> 
>> With multiple canister installations the integrity and security of the
>> actuation firing circuits becomes an issue. These must be duplicated,
>> supervised and should not be run together. The first unit  that fires may
>> cause a circuit disconnect before later units are fired thus all units may
>> not discharge.
>> 
>> The ongoing testing and maintenance does not allow checking of the firing
>> device inside the container thus one can never be certain that it is going
>> to work. This was the same problem with pyrotechnic squib actuators but at
>> least you could replace them at 3 - 5 year intervals and actually fire them
>> all off when replacing them. Micro-K didn't use an electrical filament but
>> was set off by pulling a friction plug inside the chemical. This enable all
>> actuation components to be tested up to the friction plug connection.
>> 
>> I attended training courses on Pyrogen when it first came out, but have
>> always been concerned that it can be over sold and used in unsuitable
>> applications because of the cheaper initial cost.
>> 
>> Kind Regards,
>> Russell
>> 
>> Russell Gregory Ph  03 338 4853
>> Christchurch, New Zealand
>> e-mail [email protected]
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Nicky
>> Marshall
>> Sent: Friday, 13 April 2012 11:39 AM
>> To: [email protected]
>> Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents
>> 
>> I have been looking into Aerosol systems lately so that we can advise
>> clients if these are suitable for their use.
>> 
>> As mentioned below NFPA 2010 does cover the 'system' and multiple aerosol
>> units can cover reasonable size rooms.
>> I still have concerns about the dust/particles and it is my opinion that
>> this is not a replacement for gaseous systems.  Suppliers advise the
>> particles are not of concern but there is also advice that it is not
>> suitable for applications such as tape storage arrays.
>> 
>> I have come to a conclusion of sorts that this is a cheaper option for those
>> wanting to protect information rather than equipment.
>> A full system with alarms and warning would be preferred (as per NFPA 2010),
>> but even cheaper still is just the aerosol unit with no alarms which is
>> obviously a significantly cheaper option.  But with no monitoring and
>> alarms, if no one knows the units have discharged in an unmanned room - what
>> is being achieved?  Air handling remains on and the extinguishing capacity
>> reduced ....
>> 
>> If I was recommending to a client, it would be gaseous system, aerosol
>> system, aerosol units.  In that order - decreasing cost gives decreasing
>> protection and benefits. Not to say that aerosol is less effective in fire
>> suppression as I have not been able to find that type of information.
>> 
>> Regarding the comment about large companies not producing this type of
>> product,  it also made me more wary of the product.  However I do note that
>> Ansul/Tyco used to produce an Aerosol known as Micro-K.  Not sure what
>> happened to it.  Maybe someone else on the forum could comment on this?
>> 
>> 
>> Kind regards
>> 
>> 
>> Nicky Marshall
>> Branch Manager (Blenheim)
>> 
>> Protech Design
>> Specialist Fire Protection Consultants
>> 03 579 5577
>> 021 433 488
>> skype: nicky-marshall
>> 105A Alabama Rd, Redwoodtown, Blenheim 7201, New Zealand PO Box 4022,
>> Redwood Village, Blenheim 7242, New Zealand
>> 
>> 
>> -----Original Message-----
>> From: [email protected] [mailto:[email protected]]
>> Sent: Friday, 13 April 2012 1:10 a.m.
>> To: [email protected]
>> Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents
>> 
>> Reza my friend haven't heard from you in a long while,  E-mail me off the
>> forum.
>> 
>> NFPA 2010 addresses aerosol fire extinguishing systems.  It would seem
>> however that the NFPA 2010 systems are a bit different than what Firepro and
>> the others you mentioned are offering.
>> 
>> Firepro is actually UL Listed for use in the US and approved for use by
>> other international governing agencies.   The technology has actually been
>> around for more than 30 years so it's not new.
>> 
>> The market for aerosol may be small so if there are not substantial sales
>> the big companies who are already invested in other means of extinguishment
>> probably will leave it for someone else.  It's not a matter of them not
>> "approving" aerosol since they can't approve of an item, they can only
>> choose to offer a similar item or not.
>> 
>> I would agree that the aerosol extinguishing has its place in small
>> enclosures and such.   But cost and practicality for larger volumes would
>> have to be analyzed.
>> 
>> 
>> Craig L. Prahl, CET
>> Fire Protection
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Reza Esmaeili
>> Sent: Thursday, April 12, 2012 8:30 AM
>> To: [email protected]
>> Subject: Aerosol vs Halocarbon/Inert extinguishing agents
>> 
>> Hi all,
>> Some companies are persuading the end users to use condensed aerosol fire
>> suppression systems instead of  Halocarbon/Inert extinguishing agents for
>> local application or total flooding protection.
>> I have seen many end users buying aerosol systems for server rooms/archive
>> rooms and don't use any other kind of protections.
>> 
>> The big companies like Tyco, Kidde, Fike & Chemetron are not offering
>> aerosol systems and usually say it is not a good  and even toxic! they
>> say halocarbon/Inert extinguishing agents are the only choice.
>> 
>> Aerosol manufactures are usually Asian companies like www.pyrogen.com.my
>> (Malaysia)or www.firepro.info (Cyprus) www.granit-salamandra.ru (Russia)
>> with even UL listed products.
>> Aerosol manufactures say this a new technology and much better than others,
>> they say the big companies like Tyco, Kidde, Fike & Chemetron have already
>> invested too much on halocarbon/Inert extinguishing agents and that's why
>> they are not approving aerosol systems.
>> 
>> I personally think aerosol fire extinguishing generators are good for some
>> small spaces like electrical cabinets, but they can't be used as a total
>> flooding solution instead of FM-200 system in a server room as they can't
>> penetrate everywhere like FM-200 and also they are not clean that much.
>> 
>> Thanks for sharing your valuable experience & professional comments.
>> Reza
>> 
>> 
>> 
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL:
>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
>> s/20120412/9fff7bda/attachment.html>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL: 
>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120413/50a95f1c/attachment.html>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> 
>> This e-mail transmission contains information that is intended to be 
>> confidential and privileged.  If you receive this e-mail and you are not a 
>> named addressee you are hereby notified that you are not authorized to read, 
>> print, retain, copy or disseminate this communication without the consent of 
>> the sender and that doing so is prohibited and may be unlawful.  Please 
>> reply to the message immediately by informing the sender that the message 
>> was misdirected.  After replying, please delete and otherwise erase it and 
>> any attachments from your computer system.  Your assistance in correcting 
>> this error is appreciated.
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> This e-mail transmission contains information that is intended to be 
> confidential and privileged.  If you receive this e-mail and you are not a 
> named addressee you are hereby notified that you are not authorized to read, 
> print, retain, copy or disseminate this communication without the consent of 
> the sender and that doing so is prohibited and may be unlawful.  Please reply 
> to the message immediately by informing the sender that the message was 
> misdirected.  After replying, please delete and otherwise erase it and any 
> attachments from your computer system.  Your assistance in correcting this 
> error is appreciated. 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to